Hello,
For some backstory I lived in the city and was only able to run my generator a few times, I had to replace the temperature gauge because it was a little sticky it needed a technical tap to get the needle to jump. However the temperature needle always hovered just above 190. I moved out of the city and now I have all the time to run my generator as much as I like so, I replaced it and this new gauge holds a temp around 220. My question is what should I do? Is this a normal temperature do I have a stuck thermostat or possibly is the current gauge I got a little off? Is there any way to test the gauge? Thank you.
 

Attachments

Light in the Dark

Well-known member
Steel Soldiers Supporter
4,053
6,816
113
Location
MA
That unit will read higher than stock, but understand that the gauge has nothing to do with the safety overtemp circuit... should be reading 205-210 from memory with this alternate gauge.

Here is the testing TMs on the gauge.

coolant-gauge-test.jpg
 

Ray70

Well-known member
Steel Soldiers Supporter
2,959
7,226
113
Location
West greenwich/RI
Have you checked / serviced the coolant system ever? With the gage you have it will normally read a little high as L.I.T.D said, but 220 is a bit more than that gage should be reading.
If you are running it at a light load you may be fine now, but could run into issues if you have to run a long time under heavy loads.
I'd suggest checking it with an IR thermometer and consider flushing the coolant and replacing the thermostat if you find that it is indeed running hot.
 

Coug

Well-known member
Steel Soldiers Supporter
3,204
4,842
113
Location
Olympia/WA
First step is always verify. If you still have the old gauge I'd reinstall it and see if it goes back to your old readings, just for comparison's sake.
An IR thermometer used at the sending unit in the block to verify the temp would also be very useful.
I know in my HMMWV I've had to do several replacement gauges and sending units, and every combination shows different readings, so they are more of a baseline to do quick checks at a glance if something has changed compared to normal, rather than gospel.
 

BeStihl

Member
27
29
13
Location
Kentucky
I replaced a missing gauge on my 803 with this exact model. That is exactly where it registers on my unit when up to temperature. I wondered if this was a false reading also and took measurements from the sender area and I get 200 with a fluke meter with a thermocouple. I was told by the seller that it would register about 20 degrees higher due to a mismatch of it and the sender. If you don’t read the numbers and just use the position of the needle it appears very close to the same position as the factory gauge. The difference is this gauge has a marker for 200 where the factory one reads 180, & 250 where factory reads 240.
But as previously stated, verify for yourself and know you have a separate safety circuit to shut the unit down for over temp as this gauge is only for operator reference.
 

LuckeyD

Well-known member
148
429
63
Location
Vilseck, Germany
Seems two folks using the same stuff with same results kinda sorta resolves the issue. Nominal readings in the desert at 115F outside was around 195-200 full load. The thing was designed to operate to 120, but we had warmer days. Readings usually stayed at 200-205 unless the dust plugged the radiator which was cleaned weekly there. In wet cold Germany they ran about 180. I used an IR temp reader once in a while if the reading made no sense. As time and wallet is able, you may want to match those things so you get a warm and fuzzy. Someone in the thread is using manuals; Supercool!
 