• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

MEP 802a trips overload at anything over 4000 watts

Summerpaws

Active member
Steel Soldiers Supporter
93
212
33
Location
Hampton, NH
Look in the control panel. The plugs are on the Bottom of the control panel.

First take the wire off K8-3, and measure from there to the Burden Resister. If you get nothing, then unscrew P6. Look at the schematics to see what pins to check in P6/J6.

P6/J6 can also be loose, or have a bent/burnt pin. Open the lower door s lay on your back with a light and inspect.
Ok. I found the smoking gun. I removed both wires from terminal 3, K8. Wire 166B goes to J6-3. Wire 166C goes to R12-1. I unplugged P6/J6. R12 is open circuit. R13 is 7.9 ohms. Double and triple checked readings. Seems I need a burden resister. Thoughts?

IMG_1880.jpegIMG_1881.jpeg
 

BeStihl

Member
27
29
13
Location
Kentucky
Maybe check the solder joints on the R12, might get lucky. Chase the resistance from 166 to R-12 & from there to P6/J6, maybe a wire is broken. JMO
 

Summerpaws

Active member
Steel Soldiers Supporter
93
212
33
Location
Hampton, NH
Maybe check the solder joints on the R12, might get lucky. Chase the resistance from 166 to R-12 & from there to P6/J6, maybe a wire is broken. JMO
Great minds think alike. I checked the continuity of the wires from the resisters to K8 and , I think it was pin 3 of P6. All good there.
 

kloppk

Well-known member
Steel Soldiers Supporter
2,336
4,214
113
Location
Massachusetts
I've searched and didn't find that resistor as well and a direct substitute that was previously available. An option would be to use a RE70G7R50C02 chassis mount resistor.
 

grywitt

Active member
Steel Soldiers Supporter
307
245
43
Location
Nm
I learned that a couple volts difference between phases can mean a lot on these gens. I had about 4 volts difference and didn't think much about it but once I got my contacts polished in k1 I had .2 volts difference at most. I got lucky and the problem became more pronounced and forced me to look into it more so that's how I found that I wasn't getting good contact on one of my phases.

I had looked in that k1 the day prior and thought things looked okay. I guess what I bring from this is little things can mean a lot on that circuit. I guess when you are dealing with single digit ohms a couple more makes a difference..

I've ran full load and beyond for several hours now. I'll be interested to hear what caused your problem.
 

Summerpaws

Active member
Steel Soldiers Supporter
93
212
33
Location
Hampton, NH
I learned that a couple volts difference between phases can mean a lot on these gens. I had about 4 volts difference and didn't think much about it but once I got my contacts polished in k1 I had .2 volts difference at most. I got lucky and the problem became more pronounced and forced me to look into it more so that's how I found that I wasn't getting good contact on one of my phases.

I had looked in that k1 the day prior and thought things looked okay. I guess what I bring from this is little things can mean a lot on that circuit. I guess when you are dealing with single digit ohms a couple more makes a difference..

I've ran full load and beyond for several hours now. I'll be interested to hear what caused your problem.
I checked the voltage on both sides of K1 and they were spot on. (at 4K). Good info to know for sure! My problem ended up being an open circuit on R12. Makes sense now. I am trying to find one of the illusive buggers!
 

Summerpaws

Active member
Steel Soldiers Supporter
93
212
33
Location
Hampton, NH
Oh heck. These posts weren't showing up before i wrote this. Oops. Glad you found the problem.
In a pinch you could make something like this work
Yup. If I have to. It just means that I will have to fab something up and do some soldering and shrink connecting. I'll give it a couple of days and see if anything turns up,
 

Summerpaws

Active member
Steel Soldiers Supporter
93
212
33
Location
Hampton, NH
I've searched and didn't find that resistor as well and a direct substitute that was previously available. An option would be to use a RE70G7R50C02 chassis mount resistor.
Thanks. I bookmarked the page just in case. I'm working with someone on Marketplace that may have one. He's a member here it turns out.
 

Summerpaws

Active member
Steel Soldiers Supporter
93
212
33
Location
Hampton, NH
Well, it looks like these are getting pretty scarce. I am still waiting on one guy who may have one. That said, I ordered 2 resistors from Mauser. Should be here on Wednesday. They are considerably larger than the ones that are there. I will figure something out. There is room next to the resistor panel. Rather than mounting it to the wall, I think I will make a second panel and mount both new resistors to it. That way I will have the hard work done when the next one fails. KloppK, thanks for doing the homework for me!
 

Attachments

Summerpaws

Active member
Steel Soldiers Supporter
93
212
33
Location
Hampton, NH
Mauser says my resistors will be here tomorrow evening. I will scratch my head, come up with a plan and share it. I'm thinking this may be a common repair. Thanks for all the help everyone.
 

Summerpaws

Active member
Steel Soldiers Supporter
93
212
33
Location
Hampton, NH
Well, the resistors arrived late this afternoon. Too late to install, but I did have time to assess the situation. First, they are smaller than I expected. That's great news. I took a quick look at the resistor panel and I am thinking they will fit right where they need to be. I've not decided if I need to use the stand-offs. I assume the original resistors used the stand-offs for heat dissipation. The ones I got from Mauser are finned. so I am going to assume that they will be fine. Thoughts?IMG_2126.jpegIMG_2127.jpeg
 

2Pbfeet

Well-known member
778
1,530
93
Location
Mt. Hamilton, CA
Well, the resistors arrived late this afternoon. Too late to install, but I did have time to assess the situation. First, they are smaller than I expected. That's great news. I took a quick look at the resistor panel and I am thinking they will fit right where they need to be. I've not decided if I need to use the stand-offs. I assume the original resistors used the stand-offs for heat dissipation. The ones I got from Mauser are finned. so I am going to assume that they will be fine. Thoughts?View attachment 953787View attachment 953788
In a pure WAG, I would use insulated standoffs. I suspect that the originals were on standoffs for two reasons; one to reduce heat load into the support, and two in case of resistor failure, to keep them from shorting to the chassis. It is the second thought item that would make me want to keep them off the support plate.

All the best, 2PbFeet
 
Last edited:

Summerpaws

Active member
Steel Soldiers Supporter
93
212
33
Location
Hampton, NH
In a pure WAG, I would use insulated standoffs. I suspect that the originals were on standoffs for two reasons; one to reduce heat load into the support, and two in case of resistor failure, to keep them from shorting to the chassis. It is the thought item that would make me want to keep them off the support plate.

All the best, 2PbFeet
Thanks for that. I have seen the engineering files for that resistor and it looks to be very well isolated, electrically. These resistor housings are aluminum or some alloy. They are finned and machined flat on the bottom. These are designed to mount on a metal surface which will aid in the heat dissipation. I am heading out now to mount one. I'll check in when I'm done.
 
Top