Sorry for the slow reply. Helping 4 people simultaneously with generator issues around the US this evening.
The START voltage signal comes from S1-7 and goes to TB5 terminal 14. In total terminal 14 will have 4 wires on it. Two on the top screw and two on the bottom screw.
The wire numbers for the 4 wires on TB5-14 are...
140A From S1-7
140B to K12-8 (feeds the Starter circuit)
140C to K15-A (feeds the Flashing circuit)
140D to the diagnostic connector on the outside top left.
Try disconnecting all wires from TB5-14. See if CB1 still pops.
If it doesn't then reconnect wire 140A to TB5-14 and see if CB1 pops.
If it doesn't then reconnect wire 140B to TB5-14 and see if CB1 pops.
If it doesn't reconnect wire 140C to TB5-14 and see if CB1 pops.
If it doesn't reconnect wire 140D to TB5-14 and see if CB1 pops.
jaybird67k
24
Texas
140A From S1-7
It will probably be Monday before I can fool with it since I'm busy tomorrow. Thanks Kloppk for the detailed instructions.
I'll keep you updated. Is there anyway I can get a moderator to change the thread title to cb1 instead of cb3 ?