Greetings from a Newbie. Been lurking around for a while and I've learned a great deal about MEP generators from your posts and comments.
I recently bought a MEP-803A from GL which did not have the circuit protection fuse. 2 diodes in the voltage regulator were burned out (now replaced) Phase to Neutral voltage is 19 VAC. Voltage phase to phase is 38 VAC.
After a multitude of tests, I've come to the conclusion that the Q1-Q2 winding is shorted. Voltage produced is approx 1 volt. Resistance hovers around .5 ohms when hot and 1.2 ohms when cold.
The stator, rotor, exiter stator, exiter rotor and rotating diodes all test out good. Stator windings I could see from the open back plate all look good. No burn marks, no brown paint.
I was thinking of replacing the voltage regulator with a universal voltage regulator, Power Tronics XR8 comes to mind. Rep says that their VR is powered with 120 volts from the stator, no need of the Q1-Q2 leads. Has anybody ever tried a similar approach? Your comments would be appreciated.
Also, if anybody knows the nominal exciter voltage for this unit, it would be appreciated.
The engine side of the generator is in great shape. 400 hours on a tier 2 reset. No smoke, no leaks, no knocking. Starts right up. What a gem! I love diesel engines, having owned diesel cars for many years. This small Lister Petter is a winner. These generators are very impressive machines!
Another plan would be to replace the stator assembly and possibly the voltage regulator. (I can't test my "repaired" VR so it might be necessary to get a new one). If anybody has good used parts in stock, please let me know.
Thanks for your help.
Pete
I recently bought a MEP-803A from GL which did not have the circuit protection fuse. 2 diodes in the voltage regulator were burned out (now replaced) Phase to Neutral voltage is 19 VAC. Voltage phase to phase is 38 VAC.
After a multitude of tests, I've come to the conclusion that the Q1-Q2 winding is shorted. Voltage produced is approx 1 volt. Resistance hovers around .5 ohms when hot and 1.2 ohms when cold.
The stator, rotor, exiter stator, exiter rotor and rotating diodes all test out good. Stator windings I could see from the open back plate all look good. No burn marks, no brown paint.
I was thinking of replacing the voltage regulator with a universal voltage regulator, Power Tronics XR8 comes to mind. Rep says that their VR is powered with 120 volts from the stator, no need of the Q1-Q2 leads. Has anybody ever tried a similar approach? Your comments would be appreciated.
Also, if anybody knows the nominal exciter voltage for this unit, it would be appreciated.
The engine side of the generator is in great shape. 400 hours on a tier 2 reset. No smoke, no leaks, no knocking. Starts right up. What a gem! I love diesel engines, having owned diesel cars for many years. This small Lister Petter is a winner. These generators are very impressive machines!
Another plan would be to replace the stator assembly and possibly the voltage regulator. (I can't test my "repaired" VR so it might be necessary to get a new one). If anybody has good used parts in stock, please let me know.
Thanks for your help.
Pete