benjcallahan
New member
- 6
- 5
- 3
- Location
- Fairbanks, Alaska
MEP 803a. Fuel pumps run. Starter will not turn over using S1. Dead Crank operates normally. No power at terminal 7 on S1 when in start position. No voltage at starter solenoid post 2 when starting. No power at common posts 6 & 8 on S1. No voltage between pins F and J on diagnostic connection points.
I am getting no continuity at CR1 (Reverse Battery Diode) but I have anther machine that is operating properly that shows the same reading, probably operator error.
My latest idea is the voltage regulator is bad. I will swap with the machine that is functioning in the morning.
Machine did tip onto its back when moving into the garage as it is on a trailer that is back heavy. Run great last summer. Any advice would be greatly appreciated!
I am getting no continuity at CR1 (Reverse Battery Diode) but I have anther machine that is operating properly that shows the same reading, probably operator error.
My latest idea is the voltage regulator is bad. I will swap with the machine that is functioning in the morning.
Machine did tip onto its back when moving into the garage as it is on a trailer that is back heavy. Run great last summer. Any advice would be greatly appreciated!