MEP-804a preheat

calucyk

New member
13
12
3
Location
Fort Worth, Texas
New to the forum. Bought first military generator. Excellent machine. Ran load bank last weekend. Machine ran at 61amps comfortably.

This forum has been extremely resourceful. TM’s equally helpful.

That said, I have a question regarding preheat. When I turn S1 to preheat, the starter engages and the engine starts. The couple of times I tested preheat, the temperature was 60 degrees or higher. I was expecting no starter engagement or engine start, just silence while the glow plugs warm. Further, turning to start position should engage the starter and engine start. Does all MEP-804a generators operate like this?

thanks in advance. Tony
 

DieselAddict

Well-known member
Steel Soldiers Supporter
2,482
1,881
113
Location
Efland, NC
Welcome to the forum!

The starter shouldn't engage in preheat. I recommend taking the TM and going over the wiring on S1 to make sure someone didn't put a wire in the wrong place. When you take a look at the switch you'll see plenty of extra terminals where someone can put a wire that shouldn't be there.
 

calucyk

New member
13
12
3
Location
Fort Worth, Texas
Welcome to the forum!

The starter shouldn't engage in preheat. I recommend taking the TM and going over the wiring on S1 to make sure someone didn't put a wire in the wrong place. When you take a look at the switch you'll see plenty of extra terminals where someone can put a wire that shouldn't be there.
Roger that. Per the TM schematic, locations 2, 4, 6, and 8 are hot. On mine, 4 and 8 are bridged and have wires on them. Need to trace those wires to their end points. On the other side of S1 is 1, 3, 5, and 7. 1 and 7 are bridged with a diode - need to check direction, but as I read the schematic, the starter would not operate in the S1 start position, if the diode is reversed. Mine works, so diode must be in correct direction. 1, 3, 5, and 7 each have a wire. Need to trace those to their end points.

Anything sound off based on above?

Thanks, Tony
 

calucyk

New member
13
12
3
Location
Fort Worth, Texas
S1 Switch​
From​
Wire #​
Switch contact #​
Wire #From
J6-23​
139C​
1 2​
136D​
CB1-1​
TB6-4​
137N​
3 4​
136C​
P4-4​
J7-8​
118B​
5 6​
136B​
S2-2​
TB5-14​
140A​
7 8​
136A​
J3-U​
CR4 diode is mounted between terminals 1 and 7. The Positive side is attached to terminal 7.​
Thanks Guyfang. Very helpful. Once the rain stops, I will verify S1 wiring and then report my findings (and most likely success). Thanks, Tony
 

calucyk

New member
13
12
3
Location
Fort Worth, Texas
Thanks Guyfang. Very helpful. Once the rain stops, I will verify S1 wiring and then report my findings (and most likely success). Thanks, Tony
Guyfang, I compared your chart wire numbers and termination points to the TM schematic PDF posted here ( (2) All the TM's you need to work on the MEP-804A | SteelSoldiers ). See page 21. The wire numbers and termination points do not match. Is it possible the schematics posted at the link above do not apply to my machine? I can't rule out I'm reading this wrong. Any advice before I start moving my S1 wires to match either schematic?
 

calucyk

New member
13
12
3
Location
Fort Worth, Texas
Attachment is for the S1 wire hook up.

Guyfang, I compared your chart wire numbers and termination points to the TM schematic PDF posted here ( (2) All the TM's you need to work on the MEP-804A | SteelSoldiers ). See page 21. The wire numbers and termination points do not match. Is it possible the schematics posted at the link above do not apply to my machine? I can't rule out I'm reading this wrong. Any advice before I start moving my S1 wires to match either schematic?
 

calucyk

New member
13
12
3
Location
Fort Worth, Texas
You are right! Wrong picture. I was having problems coping and grabbed the wrong switch. Sorry. Here is right out of the book.

View attachment 849659
Problem solved. Wires 172A and 190A were reversed; 172A was on S1 7 and 190A on S1 1.

Last question related to glow plugs and the original problem. When I move S1 to the preheat position, it initially makes a click sound. It sounds like two energized points closing. Is it normal in preheat to make an initial (low) click sound? Thanks again, Tony
 