Also look at the wires from the main gen to see if they have been hot.
Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!
@Captain Ray Paul would you be so kind and open the doors to the left and right of Genset and take clear pictures of each compartment? We also would like to see a closeup of the reconnection board and the K1 contactor terminals
@Captain Ray Paul would you be so kind and open the doors to the left and right of Genset and take clear pictures of each compartment? We also would like to see a closeup of the reconnection board and the K1 contactor terminals
Ok give me a minute no problem.@Captain Ray Paul would you be so kind and open the doors to the left and right of Genset and take clear pictures of each compartment? We also would like to see a closeup of the reconnection board and the K1 contactor terminals
Ok give me a minute no problem.
Thanks MateIf you still have a short, then its in the main gen. Would like to work longer, but someone is standing here with a club. Later!
Same result.Thanks @Captain Ray Paul
View attachment 920015
this is the area off most interest at the moment
K1 is to the left of the reconnection board and the current transformers are to the right.
Please check this area carefully for burnt and or loose / frayed wires.
disconnect the three large wires from K1 facing out, leave the three 16 ga wires on K1 and test Genset again
for safety reasons, tape the the connectors on the large wires off temporarily before testing Genset!!!
ok, then it is time to get the manuals with the wiring diagrams out and start troubleshootingSame result.
Thanks Mate! Very much appreciated! I'll study the manuals tomorrow and report back on this thread.ok, then it is time to get the manuals with the wiring diagrams out and start troubleshooting
I am going to have to sign off for tonight
You may want to reconnect the three big wires.
Guy will be back tomorrow morning
So.. I took this part with the 12 nuts off and now the k1 works fine. I found a loose ground and now I have 120 to the convenience outlet. I got a new volt meter and it's now working. I plugged in my heat gun to the convenience plug and my%usage gage indicated correctly.Slow down here. Leave the three cables off. Take the three off on the other side, and tape them REAL GOOD up. Then start the set, and try to close the K1. lets see if K1 is going to close with no AC voltage on the in or output of the K1.
I plan on removing the 4 mount bolts and looking behind to see if anything is wired wrong,loose, or missing. Beyond that I'm going back to the TMs. At least I've got this far! LolGood Job!!
That is TB1. Often when people remove it from the mounting place, a wire gets pushed out of place. Then you have a short. Thats what we would have found if you had removed the K1 wires. Another GOOD way to find a short is this. Fire up the set, at about 23:00. Lights out, all the doors open. Try to turn on K1. you would have seen the arc, in the dark. Did you check ALL the connections? If not, you might want to do that.
I can see that for sure, I will definitely look into this! Thanks for the advice.Someone moved the reconnection board and when they reinstalled it they over tighten it which caused the stud to spin. Usually it breaks the eyelid attached to the stud and grounds out.