MEP 804B 805B Unbalanced Load

nextalcupfan

Well-known member
348
507
93
Location
NW Missouri
First, I want to thank everyone for being so helpful!

Is anyone running two central AC units on one 803A, if so what are their size/amps drawn, soft start kit needed, etc.? AC only, no heat, I’m in Louisiana. Thanks!
I actually did a test a month ago that's pretty close to what you're asking.
I put a 5000 watt 240 heater on my 803a 20-21 Amps) which is the equivalent to a 3.5 ton AC.
Then I turned on my 3 ton AC (15.2A power draw 77A inrush).
Ohh also it was running the rest of the house of course.

My LED lights did flicker off and on once, but other than that my 803a handled it like a champ.

I will recommend a soft start for both AC's in your case, if both of yours come on at exactly the same time you could have a problem.
 

m32825

Active member
224
171
43
Location
Central Florida
803a here. We have two units, 3 ton and 3.5 ton. We've run the whole house for days. If we want to run another 240v load (dryer, water heater) we turn off a unit. No soft start, but I like the idea and am planning to add them.

-- Carl
 