• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

MEP-805B 30kw wont stay running

peapvp

Well-known member
Steel Soldiers Supporter
1,242
1,555
113
Location
Basehor, KS
One last thing - when adjusting brightness/contrast on Monochrome LCD, turn on the backlight - it will greatly enhance the live of the LCD - as higher the brightness is set as faster the LCD will wear out.......
 

peapvp

Well-known member
Steel Soldiers Supporter
1,242
1,555
113
Location
Basehor, KS
New Heatsink Paste with 0.050” square Aluminum spacer since the old paste was dried out and no longer transferred the heat and the correct battery holder heavy duty vibration resistant with high grade CR2032 Lithium Battery
FB964998-91B1-4CC8-A7AF-5F33BBCF5EFF.jpg35D77E4A-2F41-46E6-BD54-66551807171B.jpg
 

peapvp

Well-known member
Steel Soldiers Supporter
1,242
1,555
113
Location
Basehor, KS
Update

We did some more testing / troubleshooting yesterday with the repaired CIM and the focus shifted swiftly to the A5 Board as the initial problems were still present.

The A5 has the operational Brain on it. It's a 8 bit Microchip PIC 17C44 40 PIN Plastic Dip with 8K memory and several A/D Converters and UART as well as I/O Micro Controller.

The relays for fuel pumps, starter, excitation, Network Failure Indicator and all Status LED's on Backplane are controlled by this PIC (we just call them PIC's). He also scans the Start / Stop / Run Switch, Main Contactor Switch, Fault Reset Switch etc.

Since the Device has only so many PIN's, CMOS Multiplexers are usually used. Those are the plastic DIP's with 74HCxxx

One of those who drives the relais / relais drivers is shorted.

The problem in detail:

When the Master Control Switch is set to On:

1. The Network Indicator Light comes on immediately (Before CIM even starts to boot)

2. The Fuel Pumps come on immediately

3. Other Relays come on as well (we didn't further investigate, as the problem is one of the 74HCxxx chips)

4. The CMOS Battery LED comes on immediately

CIM Boots normal and does not display any errors (except overspeed / undervoltage error from previous run which is stored now)

When Fault Clear Switch is activated either after Boot or with S2 in RUN / Prime Position it will clear any error codes on CIM but the Network Failure Indicator will not turn off

The PIC communicates with the CIM and an additional PC (if hooked up) via RS232 - both CIM and PC are slaves to PIC

All A/D D/A conversions are done by PIC and then sent to CIM / PC for display

All sequencing for operation is done by PIC according to S2 switch settings. All Analog Signals from sensors are fed to PIC except MPU which goes straight to Governor Control Board

I will post more details when I get A5 Board here for repair

Note: the software for the PIC was written in Assembler
 