After the good discussion in this thread I’ve revised my design a little bit. Below is the diagram of what I’m planning on doing. Welcome any comments and suggestions.
View attachment 886327
After the holidays I plan to start ordering the bits and get this install rolling before we have a serious outage and I have 15kWs sitting in the driveway I can’t use. Just last week there was a nasty car accident that took out a pole and the other side of the state road lost power for 18-24hrs overnight with temps in the low 20s.
I’ve also been reading the NEC some. My county has adopted NEC 2020, and while I haven’t decided if I’m pulling permits I do want to ensure that this install is fundamentally safe, and meets code. I have a few questions that I’m sure some of you will probably know the answers too. I’m also probably going to call the electrician that wired the house and pay him a few hours time to review this and do a walk through after I install.
Questions:
-with the 3P transformer is this still considered a non-SDS source? The GND is continuous across the system, but neutral now is not. The only earth ground is the service entry, and the only L0-GND bond is at the gen service terminals on the primary side and in the panels on the secondary side. To meet code would this need to be a SDS source and have a separate earth ground at the gen and break the ground at the transformer?
-I’ve fused L1/L2/L3 at 60A and running 6AWG THHN on the secondary side rated at 75A. Should I bump up the L0 conductor since many of the loads will be 120v loads using the neutral?
-NEC states that gens must be UL listed. Pretty sure MEPs are non-UL, can anybody confirm? This seems like an instant permit fail on a technicality.
-NEC requires a generator disconnect, does the MEP built in contactor meet this requirement? I included a fused disconnect incase it doesn't, and having it is probably a good idea anyways.
-THHN/THWN-2 is rated for dry and damp locations, this should meet NEC requirements for wiring in outdoor NEMA 3R and NEMA 4 enclosures, correct?
-Will the distribution panel breaking out the 3P to the separate panels meet NEC if done with UL insulated mechanical lug / multitap wire connectors?
-Other than conduit what is a good way to bundle/group the THHN inside the house and provide strain relief at the enclosures clamps? Split wire loom?
-It shouldn’t matter what order I connect the 3P legs to the transformer on the primary or secondary, as I don’t care about the phasing, and any 2 legs will always be 120deg apart, correct?
-It shouldn’t matter which leg I ‘double tap’ and send to both panels, as all the legs ae equal in the MEP stator, correct?
Other gen NEC specific things I’m tracking:
-conductors must be rated at 115% of gen face plate (52x1.15=60A)
-over current protection on primary and secondary sides of transformer
-PVC conduit must be buried 18”, and conduit can only be 50% full by volume
Thanks all.