MEP 806A Frequency gradually climbing on its own

Austin2406

New member
4
1
3
Location
KS
Gradually climbes to about 450hz to 460 hzat about 1 hz per second immediately after start up. We've checked MPU & GCU. Both are working correctly
 

Guyfang

Moderator
Staff member
Moderator
16,766
24,080
113
Location
Burgkunstadt, Germany
How long have you had the set? Or better said, how long did it work right?

Have you done any work on it? Changed any parts? Removed or replaced anything? Engine or control cube?

How did you check the GCU? IAW the TM?
 

Ray70

Well-known member
2,595
5,909
113
Location
West greenwich/RI
Well, the 12,000 rpm thing was a joke, but you guys lost me somehow.... This is an 806a running at 450Hz? what am I missing?
Thought the 806a was a 60Hz machine and the 816a designation was 400Hz.? This is an 806a running at 400+Hz?
Have the earth's magnetic poles flipped?? What gives?:unsure: Please explain where I went off the rails... Cause checking the TM didn't help me. ;)
 

Guyfang

Moderator
Staff member
Moderator
16,766
24,080
113
Location
Burgkunstadt, Germany
Did not realize you were kidding, as I have had people tell me that same thing.

That's what I am trying to find out. How that can happen. Normally can not happen. Need to know if any work was done on it of late. Need to know if any parts have been changed of late. How long it ran right. That way we can eliminate some things from the get go.
 

Ray70

Well-known member
2,595
5,909
113
Location
West greenwich/RI
Either that or he's using a cheap DMM? I once saw 400+ Hz on a cheap Chinese gen but it was due to dirty power and using a DMM.
I thought the OP meant he was reading it off the Hz gage, which blew my mind on an 806!
What are you actually seeing on the HZ gage?
 

jmenende

Well-known member
467
389
63
Location
Puerto Rico
If the engine actually slowly incerasing rpm then i would check the ip and the governor linkage. Could be stuck or just set wrong.
 

Guyfang

Moderator
Staff member
Moderator
16,766
24,080
113
Location
Burgkunstadt, Germany
Everyone needs to stop and take a deep breath here. Read and look at the TM's.

1. A MEP-806A can NOT read 400 hertz on the meter. Can not The meter only goes a little higher then 70 hertz?
2. A MEP-806A can NOT read 400 hertz on the meter. Because the Freq. Transducer can not read 400 hertz.

So where are the readings coming from? The 120 volt outlet? The load terminals?

I have to run now. So will be back later. How about some answers? And I HAVE seen a 806A produce 400 hertz!
 