• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

Mep-831 wont start the next day after finally sending power

Lettja

New member
12
7
3
Location
Vilseck Germany
Im at a loss with the tm because the troubleshooting steps are telling me to replace parts and when i do it still doesn’t work. It may be simple but i haven’t touched these since AIT and would appreciate any help.
 

Toolslinger

Well-known member
121
261
63
Location
PA
First, welcome aboard.

Never touched an 831 myself, so I can't be too much help. However, I can tell you the best thing you can do when you get frustrated with these things is to take a break, step back, and then go back to square one. Follow the TM line by line, and don't assume you did everything right. Read the step, do the step, then move to the next. It's absurdly easy to skip through, thinking you've done everything right only to find something easy. In my case I about lost my mind one day simply because I hadn't double checked the big red kill switch on my 802a.

The folks here are great, and they'll get you through this, whatever the issue is.
 

FarmingSmallKubota

Well-known member
Steel Soldiers Supporter
550
1,305
93
Location
Wapakoneta, Ohio
Im at a loss with the tm because the troubleshooting steps are telling me to replace parts and when i do it still doesn’t work. It may be simple but i haven’t touched these since AIT and would appreciate any help.
First thing is to check the E-stop, lots of little things can contribute to them not starting. lets not fire the parts cannon before we truly diagnose the unit. give us some more information. One of the most frustrating things about all of these Yanmar single cylinder engines is without prime and a little air in the system they will not run or run very poorly.
 

Lettja

New member
12
7
3
Location
Vilseck Germany
First thing is to check the E-stop, lots of little things can contribute to them not starting. lets not fire the parts cannon before we truly diagnose the unit. give us some more information. One of the most frustrating things about all of these Yanmar single cylinder engines is without prime and a little air in the system they will not run or run very poorly.
So i follow the tm troubleshooting instructions and it was fine up till the start switch and the corrective action is to pull out the estop and probe (+) on s19-a2 and (-) on tb3 test point tp31 and to flip the start switch to start and then i only get 4 volts when it says i need 20-32 vdc but i just replaced the switch with one from another genset and its still providing the same voltage. So unless both switches are broken i could only think of it being a shorted wire maybe.
 

Ray70

Well-known member
Steel Soldiers Supporter
2,827
6,822
113
Location
West greenwich/RI
The E-stop is simply a switch so all it can do is pass through whatever voltage is going into it, so I'd start by making sure the batteries are fully charged and in good condition. If the batteries are older, make sure they have good amperage and not just a surface charge, which will drop substantially as soon as a slight load is applied.

Removed my comment about the dead crank switch, I thought you had an 813, not an 831! my mistake...
 
Last edited:

Lettja

New member
12
7
3
Location
Vilseck Germany
The E-stop is simply a switch so all it can do is pass through whatever voltage is going into it, so I'd start by making sure the batteries are fully charged and in good condition. If the batteries are older, make sure they have good amperage and not just a surface charge, which will drop substantially as soon as a slight load is applied.

Removed my comment about the dead crank switch, I thought you had an 813, not an 831! my mistake...
Battery tester said it was fine and i get the proper voltage out of the estop point s19-a2
 

kloppk

Well-known member
Steel Soldiers Supporter
2,276
4,006
113
Location
Pepperell, Massachusetts
22 vdc in stop
OK, that's indicating either the battery(s) are not charged/bad OR something in the path of getting battery voltage to S19A2 is failing.

Measure the DC voltage at the following points with your meters Negative lead on TP31 (chassis ground), E-STOP pulled out and S1 in START
1) Voltage at S19-A2
2) Voltage at S19-A1
3) Voltage at circuit breaker CB1. Check both terminals
4) TP30
5) Center terminal of the Slave Connector
6) Battery positive



This is the schematic path from Battery positive to S19-A2
1739977007558.png
 
Last edited:

Lettja

New member
12
7
3
Location
Vilseck Germany
OK, that's indicating either the battery(s) are not charged/bad OR something in the path of getting battery voltage to S19A2 is failing.

Measure the DC voltage at the following points with your meters Negative lead on TP31 (chassis ground), E-STOP pulled out and S1 in START
1) Voltage at S19-A2
2) Voltage at S19-A1
3) Voltage at circuit breaker CB1. Check both terminals
4) TP30
5) Center terminal of the Slave Connector
6) Battery positive



This is the schematic path from Battery positive to S19-A2
View attachment 940999
Embarrassingly it was the battery and i had to be explained what a cca was. Im really just a part replacer so thanks for the help i really appreciate it.
 

Lettja

New member
12
7
3
Location
Vilseck Germany
I pass there every time I come on post through the Netzaberg gate. Many moons ago I worked in your MP. Well, all of them on post at one time or another.
Id be very grateful to learn if you were to stop by the next time youre around, trying to figure them out on my own isn’t working out all that well because the one set i had running just broke down in the field.
 
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks