Update.. I put a multimeter on the OP sensor and checked continuity per the TM and it tested ok. I started looking at the governor actuator arm and realized I hadn't tightened the nuts on the rod and it had spun up 3/4 of an inch form the bottom threads. Readjusted and locked nuts in place and fired it up. Everything started up and runs very well now. Low OP light goes off, and the OL/SC does not appear. Checked power on the courtesy outlet and got 120V, GFCI test worked, and then checked lugs L1-L2 was 240V and L1/L2 to N separately was 120V. Tested running a angle grinder and the engine ramped up and then ramped down after I turned it off..
Still have a couple issues:
1/ After I use S1 to "Stop" the generator, the actuator arm stays attached to magnet when I try to restart. If I move it manually away from the magnet it fires right back up. Is this a calibration I still need to do?
Video:
2/ If I let the generator run for 10 minutes then move S1 to "Stop" the generator gauges all seem to shutdown, however, the engine doesn't stop. I have to move to "Run" which throws fuel into the engine causing it to rev and then move to "Stop" and it turns off. What's weird is if I start the engine let it run only for a minute or two and then "Stop" it actually turns off. Seems like when it runs more than a couple minutes.
Video:
3/ Hour meter didn't seem to move. I saw in a different post the terminals should have 28VDC? This sound right?