Got a MEP-831A that I suspect has a bum governor controller.
Was reading the TM -13&P and I suspect there is a typo regarding voltages that should be seen on the controllers D & E LOAD input terminals.
TM 9-6115-639-13&P dated 30 APRIL 2010 page 19-1 paragraph 3. PDF page 160.
It reads...
3. Close circuit interrupter and apply full load to generator set. Voltage between terminals F and G should be 24
VDC. Voltage between terminals J and H should be 11 VDC. Voltage between terminals D and E should be 0
VDC. Voltage between terminals A and B, B and C, and C and A should be 193+/-2 VAC.
I suspect "Voltage between terminals D and E should be 0 VDC" should read "Voltage between terminals D and E should be 5 VDC".
That is what I measure when it's under full load on both my 831's and 2.5 VDC with 50% load.
Is this a TM typo?