- 2,149
- 3,536
- 113
- Location
- Pepperell, Massachusetts
The voltages need to be taken across the terminal pairs such A & B, A & C, B & C.
IE hook one meter probe to terminal A and the other to terminal B.
293 Hz is way to high a frequency/RPM for no load. You need to perform the Governor Adjustment procedure .
It's in the 13&P TM.
If you can't achieve 254 Hz at no load then your Governor Controller module is probably toast. They fail frequently.
IE hook one meter probe to terminal A and the other to terminal B.
293 Hz is way to high a frequency/RPM for no load. You need to perform the Governor Adjustment procedure .
It's in the 13&P TM.
If you can't achieve 254 Hz at no load then your Governor Controller module is probably toast. They fail frequently.