I am having trouble contacting the load on my 831. When the generator is running, there is a green light and a constant buzzing coming from the K15 and when closing the circuit interrupter will cause the relay to burn up. If anyone has an idea on why this is happening, help would be greatly appreciated.
 

Dwnorton1

Active member
Steel Soldiers Supporter
400
23
28
Location
Healdton Oklahoma/ SOOK
You will get beat up if you post in too many places.

I responded to your other post as well. Make sure that the K15 relay is 120vac coil. Starter lockout relay. The other two ice cubes are 24vdc coils. Mine had been swapped around before I bought it. It didn't burn up the 24vdc ones but boy would it chatter.

http://www.steelsoldiers.com/showthr...-TM-for-MEP831

This will come in handy. Consider it your 831 bible.
 

Jay722

New member
10
0
0
Location
Sevierville, TN
Do you have a model or part number for the relay that needs to be used? I just tried a 120vac coil relay and it is still failing to contact the load.
 

Dwnorton1

Active member
Steel Soldiers Supporter
400
23
28
Location
Healdton Oklahoma/ SOOK
IMG_1884.jpg

RH2B-UL
AC110-120v
idec


This relay is starter cutout relay. You may have only corrected one of the issues. It still could be K 15 related, but could well be something else. I would have to look at TM. I have not chased around the contactor interlocks.
 
Last edited:

Guyfang

Moderator
Staff member
Moderator
18,071
27,109
113
Location
Burgkunstadt, Germany
Part number RH2B-UL
NSN 5945-01-509-9898
Military Cost: $14.00

Manufacturer:
COSPOLICH INC. 14695 HWY 61 NORCOLA70079-1111UNITED STATES

Also interesting info:

OVERALL LENGTH1 7/100 INCHES NOMINAL
OVERALL HEIGHT1 39/100 INCHES NOMINAL
OVERALL WIDTH0 819/1000 INCHES NOMINAL
ENVIRONMENTAL PROTECTIONSHOCK RESISTANT AND VIBRATION RESISTANT
END ITEM IDENTIFICATIONSLIDE ASSY; SEAWOLF CLASS SSN
FREQUENCY IN HERTZ50 MINIMUM AND 60 MAXIMUM
WINDING QUANTITY1
COIL QUANTITY1
DUTY TYPECONTINUOUS
MOUNTING FACILITY TYPE AND QUANTITY1 PLUG-IN TERMINAL SINGLE MOUNTING FACILITY
NONPILE-UP MAIN CONTACT ARRANGEMENT2 POLE, DOUBLE THROW, ONE POSITION MOMENTARY
OPERATING VOLTAGE RATING AND TYPE AT SPECIFIED TEMP120 VOLTS -80 DEG FAHRENHEIT TYPE 9F SINGLE WINDING
MAIN CONTACT LOAD CURRENT RATING AT MAXIMUM RATED VOLTAGE10 AMPERES AC RESISTIVE LOAD
MAIN CONTACT MAXIMUM VOLTAGE RATING IN VOLTS120 AC
TERMINAL TYPE AND QUANTITY8 TAB W/SCREW ALL FUNCTIONS
 