• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

MEP Generator Output Waveforms and THD

kloppk

Well-known member
Steel Soldiers Supporter
2,148
3,526
113
Location
Pepperell, Massachusetts
In another thread people were interested in how clean the AC output was from various generators as compared to utility power.
Below is a compilation of various AC power source waveforms and Total Harmonic Distortion (THD) calculation results.


Function generator set at 60 Hz. "Ideal" AC waveform.
Function Generator.jpg


Utility Power - 2.4% THD
Utility Power.jpg




MEP-831A with factory Inverter. No Load- THD 1.1%
831 Inverter.jpg


MEP-831A with factory Inverter. 100% Load- THD 1.0%
831 Inverter 3 Kw.jpg





802A No Load - THD 2.7%
802.jpg


802A - 3 KW Load - THD 3.5%
802 3 Kw.jpg




MEP-1030 No Load - THD 2.6%
1030 Waveform.jpg


MEP-1030 3 KW Load - THD 3.0%
1030 Waveform 3 Kw.jpg




MEP-831A with PMA & Inverter Swapped out and using a convention generator head in place of them.
No Load THD 4.1%
831 Head Swap.jpg


MEP-831A with PMA & Inverter Swapped out and using a convention generator head in place of them.
Under full load. THD 11.9%
Strange as the waveform looks cleaner...
831 Head Swap full load.jpg
 
Last edited:

Icesythe7

Active member
147
223
43
Location
Indiana, USA
In another thread people were interested in how clean the AC output was from various generators as compared to utility power.
Below is a compilation of various AC power source waveforms and Total Harmonic Distortion (THD) calculation results.
All tests done with generators unloaded.

Function generator set at 60 Hz. "Ideal" AC waveform.
View attachment 904567


Utility Power - 2.4% THD
View attachment 904573




MEP-831A with factory Inverter - THD 1.1%
View attachment 904575



802A - THD 2.7%
View attachment 904577





MEP-1030 - THD 2.6%
View attachment 904579




MEP-831A with PMA & Inverter Swapped out and using a convention generator head in place of them.
THD 4.1%
View attachment 904581
Perfect and thanks for the results, I figured the 831a would be the cleanest with an inverter and the dirtiest without one since single cylinder engine, however when you get time can you post the 831a under a load aswell as that is obviously when the distortion matters, 3-4% is pretty typical on unloaded single cylinder non inverter generators but under a load where it is harder to maintain a constant engine rpm will show how good/bad it can really perform.
 

WWRD99

Well-known member
Steel Soldiers Supporter
1,117
1,715
113
Location
York Pa
That's nice to know! Is the 803 about the same sine as the 802?

Sent from my SM-S906U using Tapatalk
 

Icesythe7

Active member
147
223
43
Location
Indiana, USA
That's nice to know! Is the 803 about the same sine as the 802?

Sent from my SM-S906U using Tapatalk
The 803 should be a bit better than the 802(probaly only noticeable under a load as no counter magnetism slowing down motor under no load), what causes the distortion is the engine slowdown/speedup inbetween powerstrokes of each cylinder so generally the less downtime of a powerstroke the more smooth the engine runs and therefore rotor spins xd, hopefully when klopp has time he can put some side by side comparisons up of loaded gensets as that is where it obviously matters since under no load nothing is plugged in anyways.

anything ~5% or higher is generally unsafe to anything sensitive but obv anything near that will probably start taking a little life from the device, so 1-2% under a load would be crazy good and that is why inverters are the best!
 
Last edited:

Icesythe7

Active member
147
223
43
Location
Indiana, USA
Added to the original post
11.8%!!! oh lord thats worse than my harbor freight predator 9000 at full load (9.6%), we now know what not to plug sensitive devices into haha...very much appreciate you taking the time to do this I wanted alot of this info for awhile now but only have an 803!
 

Digger556

Well-known member
Steel Soldiers Supporter
268
608
93
Location
Denver CO
Thanks for the data points! I've been wanting to revisit this and quantify the THD, so you are saving me a lot of effort.

Here a comparison to some other generators and inverters I did previously:
 

kloppk

Well-known member
Steel Soldiers Supporter
2,148
3,526
113
Location
Pepperell, Massachusetts
11.8%!!! oh lord thats worse than my harbor freight predator 9000 at full load (9.6%), we now know what not to plug sensitive devices into haha...very much appreciate you taking the time to do this I wanted alot of this info for awhile now but only have an 803!
I'm redoing that test. Will revise original post when I can today.
 

Digger556

Well-known member
Steel Soldiers Supporter
268
608
93
Location
Denver CO
How did you calculate THD with that scope? I have a Rigol DS1054Z and I think the only good way to do it is export the raw data.
 

Digger556

Well-known member
Steel Soldiers Supporter
268
608
93
Location
Denver CO
Used the scope to do an FFT on the waveforms, measured the amplitude difference between the fundamental frequency and the harmonics. Then run that thru a spreadsheet to calculate THD.
Okay, I can do that with mine. Thanks!
 

Icesythe7

Active member
147
223
43
Location
Indiana, USA
Historically, Military gen sets have almost always a clean waveform.
mep-831a is the cleanest by far, since single cylinder I'm sure that's why they decided to use an inverter...its a shame they are a pita, I am looking to buy one on sunday fully working for $800 (hopefully) and was curious the THD if/when I am forced to swap out the inverter but if it is going to be that high there is no reason (for me atleast) to do the swap for what I plan to use it for.
 

Triple Jim

Well-known member
1,376
291
83
Location
North Carolina
I'd be interested in knowing what devices are sensitive to harmonic distortion. I've run desktop and laptop computers on square wave inverters for many hours with no problem, and a square wave has more than 40% harmonic distortion. Motors generally don't care about a few percent, since they're so inductive that they effectively filter out higher frequencies. In general, electronic devices like computers and sound systems have a power supply to convert line voltage to the DC that actually runs them, and those power supplies are very forgiving.
 

DD58

Well-known member
148
345
63
Location
Connecticut
Wow so not bad but not great. I’ll keep this in mind and only run it to 70% won’t run the TVs on it just the fridge and the ac units of need be. I’m going to have to get an 802 and call it a day


Sent from my iPhone using Tapatalk
 

Icesythe7

Active member
147
223
43
Location
Indiana, USA
I'd be interested in knowing what devices are sensitive to harmonic distortion. I've run desktop and laptop computers on square wave inverters for many hours with no problem, and a square wave has more than 40% harmonic distortion. Motors generally don't care about a few percent, since they're so inductive that they effectively filter out higher frequencies. In general, electronic devices like computers and sound systems have a power supply to convert line voltage to the DC that actually runs them, and those power supplies are very forgiving.
There is a nice write up here https://electrical-engineering-portal.com/harmonics-influence that will explain the negative effects on multiple different types of devices like even normal motors will run hotter than normal, degradation of fuses etc

It isn't that all these devices will not run on dirty power it is just that it will cause premature wear that is generally avoidable...you can run your car for many thousand miles without an oil change even many years but it will eventually sludge up and destroy the motor earlier than with proper oil changes, like you said the power supplies in pc's/tv's etc are indeed forgiving but no reason to knowingly feed them dirty power unless it is necessary or if your don't care to replace them earlier than needed.
 
Last edited:

DieselAddict

Well-known member
Steel Soldiers Supporter
2,532
2,059
113
Location
Efland, NC
I think most items that would be affected to the point of concern have gone out of favor (analog radio and TV being ones that come to mind). I know there are concerns with running sensitive medical equipment on low quality power. All I could say is to follow the manufacturers advice with that stuff.

Now with most things being driven from switch mode power supplies, the probability of damage is pretty much gone.

As mentioned above the main effect is some additional heating. If you aren't running the equipment at its limits there isn't much to worry about.
 

Digger556

Well-known member
Steel Soldiers Supporter
268
608
93
Location
Denver CO
Much ado about nothing. If we are powering a 1.4 billion dollar Patriot Battery, or a Hospital using state of the art medical equipment, using Military gen sets, I really doubt that the power is very "Dirty".

My local utility power was more distorted than what my 802a was producing. I consider the TQGs to be "clean" power.
 
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks