1,500 watts ÷ 28 volts = 53 amps. Even with some overload capacity of the 28v generator, it seems a bit low to be able to start an 003A. If it's been done and I'm wrong, I'll take it all back. :-D
 

Guyfang

Moderator
Staff member
Moderator
18,212
27,366
113
Location
Burgkunstadt, Germany
You are probably right. Come to think of it, I have never started one without batteries in it. Normally, we just hooked it up waited 5-10 minutes and then fired it off. Need to see what the starter pulls for amps. Been too long for me to remember what it was.
 

DiverDarrell

Member
Steel Soldiers Supporter
629
24
18
Location
Port orchard, WA
I light off my gens 802&803 once a month. Hook up some heaters for load and let run for 15min. Seems to get the batteries back up over 25v. In addition to keeping everything lubed. Walmart has 1500w heaters for $10 each
 
Last edited:

Guyfang

Moderator
Staff member
Moderator
18,212
27,366
113
Location
Burgkunstadt, Germany
Jim,

The total draw and hold amperage test for the starter is 25 Amps. But I THINK that's for a bench test, so it will be higher when installed on the set. I have not found anything else in the TM's to answer the question. So I will say that I don't know, but will try and ask someone smarter then me.
 

Chainbreaker

Well-known member
1,832
2,112
113
Location
Oregon
do you think the 1.5 will start an MEP oo3a even if the MEP 003a doesn't have any batteries?
Not sure of your intent, however I seem to recall reading somewhere on this site that you are not supposed to disconnect the batteries while the genset is running. I thought it had something to do with the voltage regulator not having a load on it. So if you were able to start a MEP-002a/003a without batteries and then disconnect the slave source that would be the same as disconnecting a battery. Am I right or confused about that?

BTW, Happy New Year everyone! May we all remain safe, warm, dry and powered up!
 
Last edited:

Triple Jim

Well-known member
1,394
337
83
Location
North Carolina
I believe the problem with running an 002A or 003A without a battery mainly comes from the noise suppression capacitors in various places like the fuel pumps and on the regulator itself. With the stock regulator, and without a battery, the capacitors are forced to try to filter the rectified but unfiltered DC from the regulator, but they're too small to succeed, so they get hot and fail. There may be other oddities from running the control system on unfiltered DC, but I don't know of anything else that would actually be damaged. Just because I don't know of anything else doesn't mean there isn't anything else though.
 

justacitizen

Active member
408
40
28
Location
oklahoma
I may be wrong,but i think if you run an MEP 003a or 2a without the batteries it will overheat the DC voltage regulator. i was of the opinion there is an aftermarket VR for the DC that can be used that allows the set to be run without batteries. again i may be wrong
 

justacitizen

Active member
408
40
28
Location
oklahoma
Thank You! I wonder how many amps it takes to start an MEP 003A? would a gear reduction starter make a difference?


1,500 watts ÷ 28 volts = 53 amps. Even with some overload capacity of the 28v generator, it seems a bit low to be able to start an 003A. If it's been done and I'm wrong, I'll take it all back. :-D
 

Scar59

Active member
Steel Soldiers Supporter
2,811
42
38
Location
Mt. Eden, KY
I have been thinking about getting a military surplus 28 volt generators as a battery charger and as a jump starter for my 24 volt stuff. has anyone ever used one?
Yes, I have two units that I use. Great little generator (28v). Won't start a stone dead truck but will charge up low batteries in about 10 minutes. Starts a 002/003 with no problem. Haven't tried a generator without batteries. A buddy of mine has several in stock, PM if interested.
 

STLvortac

New member
22
0
0
Location
St. Louis, Missouri
On the subject of solargizers, do they have any drain on the battery when not exposed to the sun? I know my 12v battery maintainer warns against leaving it connected to the battery if not plugged in to AC.
 