Correct
Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!
It cant start. When you have just the A&B jumped, it will only turn over the engine, not start. For it to start it then has to reverse the S9-1 contacts, at about 300 RPM.Did speed switch a to b no start but it did crank.
Guyfang did you say you rebuild the A11s?It cant start. When you have just the A&B jumped, it will only turn over the engine, not start. For it to start it then has to reverse the S9-1 contacts, at about 300 RPM.
This below is from the MEP-006 book, but its the same as your set.
14-17. General.
a. The speed switch, driven by the camshaft
through a tachometer drive assembly and an angle
adapter, provides sequenced control of circuits during
engine startup and protection against engine over speed
during operation. Three sets of contact elements, S9–1,
S9-2, and S9–3, contained in the speed switch, are set
to open, close, or transfer by centrifugal force at certain
engine speeds. The speed switch drive gear is designed
to drive the speed switch at one–half engine speed
b. At an engine speed of 580 to 620 rpm (accelerating)
element S9–1 transfers two sets of contacts,
energizing the field flash circuit and de-energizing the
crank relay to stop the starting motor.
On Class 1 sets, when the engine reaches the
speed range of 1180 to 1220 rpm (Mode I); 1650 to 1700
rpm (Mode H) element S9–2 closes, energizing the
electro-hydraulic governor which takes over control of
engine speed.
d. Speed switch element S9-3 consists of two sets
of contacts which are set to transfer at an engine speed
of 2425 ± 25 rpm to shut down the engine and prevent
damage to the equipment. Shutdown is achieved by
de-energizing the stop-run relay and the fuel solenoid,
cutting off fuel to the engine.
2. Elements S9–1 and S9–2 reset at 100 rpm (decreasing)
below actuation speed. Element S9–3 is
manually reset by a push button on the speed switch
housing.
To get the set to run, you need to move your jumper wire on J37, (The S9 canon plug ) from pin A to B, to A to C. Yes, I know the picture shows pin D. Its a TYPO! Pin C!!
View attachment 918720
I'm pretty sure I need the transformer would you have a line on a replacement?No. Not now anyway. Back in the mid 70's, and it was mostly just replacing parts. Its easy to see whats bad. And 99% of the time it was the card. So we "found" a few bad ones, and ordered "extra" parts to repair them with. Peter has repaired A11's.
I forgot you don't live in the states have a good nite sirPeter did a rebuild thread and wrote what Trafo he bought, because the old one is not to be had. And yes you need one. The good thing, is that the Trafo for the A11 is used in both the 50-60 hertz models as well as the 400 hertz model. Most people think the 400 hertz A11 is junk, and its not. Only the VR card is different. Its closing in on 00:30 here, so if Peter doesn't come up, I can maybe try to start looking in the morning.
The transformer can be bought via our websiteI'm pretty sure I need the transformer would you have a line on a replacement?
Just another AVRHas anyone seen thisView attachment 918986
Item description from the sellerItem description from the seller
GENERAL The ADVR-073 is an advance Hybrid Analog Digital Voltage Regulator design for general generating applications. The ADVR-073 uses a reliable electronic chip in its design. This eliminates complex analogue components. In addition, over excitation and loss of sensing shutdown protections with matching U/F, O/E LED indicator lights is standard. Lastly this automatic voltage regulator prevents the generator from excitation overload, preventing excitation and AVR damage. It is easy to install and flexible for use in both shunt type and generators with auxiliary windings. BASIC SPECIFICATIONS ---Voltage sensing: ------170-520, 1 phase, 2 wire ---Frequency: ------50 or 60 hz dip switchable ---Voltage Regulation ------+/- 0.5% ---Power Input: ------Voltage 100-300 Vac 1 phase 2 wire.
Ok so no better or worse than the 054Just another AVR
Same issue as the other AVR, you need a series resistor with the exciter coil
The series resistance must equal 9 Ohm or higher
View attachment 918996
That would be correctThat I would not say. You have to compare what they do, and how they do it.
@peapvp Just curious: when you say that the "DC Field Volt / Current response" doesn't match, I think of several possibilities, not all of them bad, or good. Can you elaborate a little? Are they deficient in some way? Is it correctable? e.g. does the DC field signal have more, say for example, jitter in it that impresses harmonics on the output waveform?That would be correct
View attachment 919011
the 054 in comparison puts out a max voltage of 63VDC @ 5A continuous into the exciter but can go up to 90VDC @ 7A for up to 10 seconds to accommodate sudden load changes
However the series resistance has to be a minimum of 15 Ohm for the 054
None of the aftermarket AVR’s match the exact DC Field Volt / Current response vs the measured generated line voltage in comparison to the A11 when generator is under load and especially is getting close to 75% to 100% load range
These AVR’s are a compromise when the original A11 is not available any longer
Well this is where this starts for beginners:@peapvp Just curious: when you say that the "DC Field Volt / Current response" doesn't match, I think of several possibilities, not all of them bad, or good. Can you elaborate a little? Are they deficient in some way? Is it correctable? e.g. does the DC field signal have more, say for example, jitter in it that impresses harmonics on the output waveform?
Thanks,
2Pbfeet