• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

MEP803a Battery Charging Issue

Guyfang

Moderator
Staff member
Moderator
16,794
24,146
113
Location
Burgkunstadt, Germany
If the alternator is not putting out the right voltage, then the rubbing the post is not really going to tell you anything. Thats what I was trying to write. Its not a matter of you having a parasitic "load", or draw, on the batteries, and its draining them. Thats not your problem. The alternator will not properly charge them. Different matter.
 

925a2Tim

Member
Steel Soldiers Supporter
23
38
13
Location
Milton de
I am having the same problem with my generator and thank you all for the help everyone is providing.
I do have a simple related question,
Are they batteries just for starting or do they need to stay charged for operation of the generator
 

kloppk

Well-known member
Steel Soldiers Supporter
2,149
3,536
113
Location
Pepperell, Massachusetts
Per the -10 TM...

"Two batteries are required, one on each side of the generator set. The batteries are electrolyte serviceable, lead acid, 12 volt type, connected in series. After starting, the generator set is capable of operating with batteries removed. A diode and a fuse, located behind the control panel assembly, protect the generator set if the batteries are incorrectly connected."

So you can jump start it and run the set without any batteries installed.
Just be sure the unconnected battery cables can't come in contact with anything.
 

925a2Tim

Member
Steel Soldiers Supporter
23
38
13
Location
Milton de
Thank you for the help. I know it's all in the TM but a last minute request for a big generator left me with no time to do my homework.
Thanks again to everyone that shares their knowledge
 

Orpington13

New member
11
16
3
Location
Hartford Connecticut, USA
To me that sounds like the diodes are fused in the alternator, meaning a bad regulator.
Can you take the alternator somewhere to be tested?
Thanks for the reply. I just got the alternator back and as many suspected, the diodes and rectifier needed to be replaced. I just got the repaired alternator installed and now the ammeter never goes positive after the start. Just after the start it's maxed out on the negative side of the gauge and over the course of 10 seconds it slowly worked its way up to -2A. I let the generator run for around 5 minutes and the needle never moved above -2A. I checked the voltage across the posts on the alternator and it read 28.6V, much better than before. I checked the wiring on the alternator and it was all correct. I have seen some other threads discussing troubleshooting the battery charging system and I had gone through those checks but I'll start going through them with the new alternator installed to see if any new clues come up. If anyone has any thoughts based on the new behavior of the system I'd be happy to hear them.

Thank you,
Adam
 

zarathustra

Active member
Steel Soldiers Supporter
235
59
28
Location
glasgow,ky
Could you have the wires to the ammeter gauge connected backwards? Even with fully charged batteries the gauge should normally read high amp draw after first starting the gen and gradually head back to zero or near zero. That is exactly what your ammeter is doing, except it is starting in the wrong direction. Reversed wires would exhibit exactly what you are seeing.
 

Orpington13

New member
11
16
3
Location
Hartford Connecticut, USA
Could you have the wires to the ammeter gauge connected backwards? Even with fully charged batteries the gauge should normally read high amp draw after first starting the gen and gradually head back to zero or near zero. That is exactly what your ammeter is doing, except it is starting in the wrong direction. Reversed wires would exhibit exactly what you are seeing.
Thanks for the suggestion, that's exactly what it was. Whoever worked on the set before me labeled the wires with a + and - correctly but then installed them backwards on the gauge. I ran it for a half hour, drawing as much power as my house could ask for, and it all seemed to work fine and the batteries charged. This community is great, thanks to everyone for all the help!
 

Johncar48

Member
91
30
18
Location
Kerrville, tx
Well gentlemen I've read all the threads, I think, but I just put new batteries, new battery charge alternator on my 803, checked the wiring on the ammeter, checked fuse and the unit run great and puts out plenty of power to the house...issue is my ammeter will not go to the positive side. it's staying around -2ish. What am I missing? Could the ammeter be bad? How do you adjust the ammeter. It has an adjustment screw on the front.
 

Digger556

Well-known member
Steel Soldiers Supporter
268
608
93
Location
Denver CO
Just FYI, it's not possible to discharge only one battery because they are wired in series. A parasitic drain will draw from both batteries.

If one battery is discharging, but not the other, it's due to self-discharge of that battery, meaning the battery is bad, not the alternator.
 
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks