Thanks, I read the post a while ago where you explained that. It spurred me to go and recheck all my connections on the defective unit.The amount of work you have done, I'm betting your problem is with a mis wired hookup. I had a unit with a similiar problem and I checked everything like you. I double checked the wiring and everything checked out, then I was taking S8 out of another unit to switch them around and noticed it was hooked up alittle different. So I went and compared the 2 units and sure enough, the unit that was tripping overload had 1 wire on S8 hooked up different. Sure enough that was the issue the whole time, the wire was hooked 1 spot off. When I was verifying the wire hookup, I made the mistake of looking to fast at S8 numbers and was just glancing at the wire numbers and the S8 numbers.
I replaced both S6 and S8 in this unit last summer, wiring them per the schematic, and had a working unit right beside it to compare. I will go back over it, checking each wire number, point to point, using an inspection mirror and a good light.
The time spent on this is not a problem, I get to it when I can, weather permitting and have a working unit to rely on.
This has proven to be quite the challenge so far.....but the consolation is becoming familiar with it.
Oh well.....drink water and drive on. Will keep updating as it progresses.
If I happen to find the offending condition, I will photograph it for posterity.��