rustystud
Well-known member
- 9,169
- 2,725
- 113
- Location
- Woodinville, Washington
View attachment Scan0007.pdf This is the finished reconnection box. The diagram is how I connect the main generator cables to the TB2 buss bar. This is a "double Delta" configuration allowing the maximum use of the generators potential. To avoid confusion I used the actual cable numbers in the diagram instead of "T1 T2 T3 etc" . Later I will show how I modified the control box. The wires I used going out to the control box could have been anyone I chose it to be. I did choose to use the same wires for the field as the original. There on the side of the box is TB3 where the field wires are. P60G16 connects to P60D16 . This wire goes into the control box and connects to TB5 and wire P60A16 which goes to K1 (A1) terminal #7 . I then supply a jumper wire from this junction to the SW460 field terminal #F2 (positive) . The other wire is the field ground which ends up going to terminal #F1 on the SW460 regulator. You can use whatever wire you choose. There are plenty to use ! Again I just use P59 as it's the same field wire in the schematics . Just a note for everyone. The first 3 numbers and letters are the most important in following the schematics. The P59 wire will change it's next letter depending on it's location but it is still the same wire. So the P60A, P60G, P60D are all the same wire. I chose wires X12, X14 to be my ammeter wires for L3 and X40, X22 to be the ammeter wires for L1. Wire #17 is my voltmeter wire for L3 and X15 is my voltmeter wire for L1.
That's basically all there is to it for the reconnection box.
I should mention that on TB2 there are 3 jumpers connecting #1 and 2 then 3 and 4 then 5 and 6 .
After doing this you will have a single phase 120/240 volt generator without all the needless garbage.
That's basically all there is to it for the reconnection box.
I should mention that on TB2 there are 3 jumpers connecting #1 and 2 then 3 and 4 then 5 and 6 .
After doing this you will have a single phase 120/240 volt generator without all the needless garbage.