justacitizen
Active member
- 408
- 40
- 28
- Location
- oklahoma
i have an MEP 003A that runs strong and carry a resistive load fine but it won't start the ac condenser unit. the main breaker trips instantaneously. i installed a soft start on the unit but it made no difference. i read the whole thread about the main breakers and have done a little work to see what i have. i checked the ac output box windings in the cvt to make sure the box isn't for an 002A and since the box has four wraps it seems correct to be for an 003A. the percent of load meter seems to run higher than the load though. i read that the main breaker for an 003A is the same as for the 002A and then i read it isn't the same????? also there is an adjustment inside of the ac output box? is this to adjust the trip on the breaker? the machine runs the house,hot water tank oven dryer well pump just fine but it will not start the ac compressor no matter what even by itself. does anyone have any ideas??? Thanks the ac condenser runs at about 24 amps on main power i will get the starting amps and return.