The shutters on my MEP-003A genset never open unless the load is significant. In 50 deg weather, I don't think mine would ever open. However, when the load is high in hot weather they open fine. If you need one, Delks is another source. http://www.delksarmynavysurplus.comopcorn:Well working on getting the old generator running and with alot of help she runs and powers up fine. Noticed the Thermo Power Unit Shutter wasn't opening after 15 minutes running in 50 degree weather. Pulled off the Thermo Power Unit per the manuals instructions and placed it in some heated oil - never even twitched. So now I am looking to replace it - any suggestions?
Thanks. That's what happens when I type fast and don't check the results. The abive link has been corrected.