The issue with loading via the conveinence outlet is it only draws off one winding so it could cause hunting of engine speed. It will put out over 1800 watts before tripping the breaker.
on frequency meters, they LEAK and most units have spent time outside so they rapidly corrode. There is a permanent magnet inside and rust chips are magnetic so that gums up the works.
The meter is a 200 micro ampere full scale deflection movement, I have a source of NOS movements, I can swap the scale from a failed meter onto a new movement in a new case for under $30.
If if you have a multimeter with 0-300 micro amp measurement range, you could disconnect the meter from the transducer and hook up the multimeter to see if the transducer is good. If shot, just get one of the digital reproduction meters.