The way to test for wet stacking is to add load a little at a time. Starting an AC unit is way too much load at once. You need to find that point where it struggles and hold it there till it clears then bump it up a little. 500w increments using space heaters is a good way to go. A load bank is even better if you can get access to one.I have a question regarding the wet stacking. I am not sure how much my particular unit has wet stacked. It runs well without any smoke or soot. The issue I am now having is that when I put a decent load on it the generator will stall out.
I can run all of my shop lights and one ac unit which brings it to about a 50% load then when I add a second AC unit the engine will stall out. I can see some wet fuel on the side of the engine leaking from the muffler gasket. My good Mep803a units will run both AC units and all of the lights at about 80% load
I am planning to remove the exhaust manifold and check it out but my time has been limited. Any thoughts on my particular situation?
That thing doesn't even seem to struggle at all at 120% load.Howdy,
OK, If my unit is the standard example of genset being sold.... you really need to do a 1-2 hour load test to clean out the pipes. I removed my muffler, and removed the exhaust manifold. I manually scrapped out the pathways in the head. Cleaned out the muffler as best as I could. Obviously the generator was run very lightly loaded in its prior life. When I pulled the exhaust manifold off, it was almost totally plugged with thick gooey carbon. I soaked the manifold overnight and then pressure washed it. Put it all back. Hooked it all up, started it up, and carbon flecks flew all over, ran a few minutes and then started loading it up. Got to 50% for about 15 minutes and the smoke just kept coming. Brought it up to 100% and it just kept smoking and black liquid dripping. After about 15 minutes here, the smoking was clearing up. I brought it up to 120% load, and it smoked some, but kept humming along. Stayed at 120% for 15 minutes, and then backed down to 75% load, now the exhaust is starting to clear up. Stayed here 30 minutes, went back to 120% for 15 minutes, sound and exhaust really looking much better. backed down to 75% 15 minutes, then down to 5% for a while. I then started turn things on and bouncing around with loads, the sound is much better, and now just a hint of smoke when a new load is added. I went up 25% at a time up to 125%. The whole generator is running smooth and not smoking like it first was. I gradually reduced everything back to 5%, opened the ac interrupter, waited a few minutes and then shut down. The MEP-803a is a very solid 10kw prime generator with a surge rating which I do not know the exact range, but it just kept running.
View attachment 556574
Halfway through at 120% load
https://youtu.be/FnWCyex-eGM
Ratch, can you tell me where you found that information? Normal math would indicate a 10 kw unit. I'd like to understand how they came up with that calculation.By the book, 25% should be 1250 watts on a 5kw genset. That sounds reasonable to me to create enough load to keep heat building and pressure high. I don't think the manual would say to run at 25% based on loading it over it's rated running, when the max loading could vary.
You could put in a sensing circuit that switches on a 1300 watt device when normal load drops too low.
Haa, it's something how you have to cut the wires to keep people from digging stuff out of the trash and putting it back into service. You should have also bashed the heaters with a hammer! LOLWet stacking has been a power generation problem for ever. The MEP-002 to MEP-006 sets had the same problem, if not worse. The military always allotted a generator much bigger then the job required. With good reason. Most units did not, could not and will never master, fingering loads. Most people have no idea how, and even when done right, it only takes one or two fools with a coffee pot and a microwave to spoil the figures. I once went to a communications site that had problems with the gen sets maintaining loads in the winter. After I took a pair of side cutters and clipped off the plug ends of four heaters, the problem went away.
Well, then, you have to know about the place at the bottom of the steps that sells the Rauchbier! Man that was some good stuff!I would take a picture for you guys, but now a days that is risky. The MP's and the security wiesel's like to find people who use a camera on post! Oh yeah, that got real interesting for me once in Bamberg.
Yeah, Andover, Ma. About 45-50 sets along with lots of trucks and trailers.
Howdy,I am picking up one of these same combinations this coming Wednesday.. All this talk of wet stacking makes me think I should check into that while I am giving it a once over. Now I am trying to figure out how I can load it up decently for an extended time. Most of my major appliances (except dryer) are gas.