Folks,
On our next Endeavour we will have a look at a AVR100 made in 2005

Fault:
Output voltage drops consistently after it has been adjusted to 208VAC after startup

First Step:
Dissolving Silicone based Conformal Coating

B782DFC0-FF4E-4DD9-80AC-9683BC0A40DC.jpeg
 

peapvp

Well-known member
Steel Soldiers Supporter
1,035
1,064
113
Location
Basehor, KS
Update:

Status after 24 hours of stripper bath

1FB4CFFD-08A9-49BA-A82A-091EB4D81CBF.jpeg
4E3851C5-2343-4A34-B6D7-F5F590B5D52A.jpeg

The Sticker “Made In China” was applied to the circuit board right below the small transformer and floated to the top since this area cleared already.

George Busch…….,..,
 

peapvp

Well-known member
Steel Soldiers Supporter
1,035
1,064
113
Location
Basehor, KS
What chem did you strip it with?
Hi Evvy,

sorry, but that’s something I cannot disclose.
This is 17 year old domestic Chinese conformal coating.
Hence the chunks. US made Silicone Conformal Coating dissolves fully in this Stripper.
Any commercial stripper for silicone based conformal coating {edit} will probably desolve this coating. A Chinese Stripper will probably work better {edit}.
The Conformal Coating we use is classified.

Peter
 
Last edited:

Jetcruzr

New member
1
3
3
Location
waterford, MI.
Hello peapvp,

I am working on my MEP 806B today. At initial startup, the voltage was well over 220VAC, but it steadily declines the longer the machine runs. It is now down to around 185VAC. Voltage adjustment switch as well as screw on AVR are unresponsive. Any suggestions? It seems like you are having a similar issue.

Thanks!
 

peapvp

Well-known member
Steel Soldiers Supporter
1,035
1,064
113
Location
Basehor, KS
Hello peapvp,

I am working on my MEP 806B today. At initial startup, the voltage was well over 220VAC, but it steadily declines the longer the machine runs. It is now down to around 185VAC. Voltage adjustment switch as well as screw on AVR are unresponsive. Any suggestions? It seems like you are having a similar issue.

Thanks!
Hi Jetcruzr,
Same issue.
i will post the troubleshooting and repair info here on this thread as we go along.
Peter
 

peapvp

Well-known member
Steel Soldiers Supporter
1,035
1,064
113
Location
Basehor, KS
Update:

Stripper Bath Time: 60 Hours

This conformal coating is definitely not MIL-STD
The filler you see here is app 1/3 of what was still floating in the stripper bath.

This should be a warning to anyone wanting to strip these boards in a batch stripper.
This stuff here will clog up your filters, strainers, nozzles and pump(s).
So, a large scale reconditioning of these GAC Boards (100, 102 etc) is out of the question.
Three or four resistors have to be replaced as a result of stripping
Transformer is in the oven for 24 hours to dry @ 125F

Caps have to be checked with the rest of the board

F474ED92-F4FC-44FD-8F51-2A66425B5DBE.jpeg
79CAD14C-0767-4E41-87D6-104ACFA3B770.jpeg
35B4C5D0-A85C-48A7-8D12-AF8D0F61BAD1.jpeg

More to follow, stay tuned

Peter
 

peapvp

Well-known member
Steel Soldiers Supporter
1,035
1,064
113
Location
Basehor, KS
Update:

The two ceramic smd caps are open (infinite ESR and capacitance), normal Value presumable 22nF/100V

The three electrolytic Caps 100uF / 400V show bad ESR and have capacitance range of 260uF to 270uF

The two axial Electrolytic Capacitors 47uF / 100V are good showing 47uF with good ESR (0.2 Ohm)

That's it for the moment, next update either later today or tomorrow

Peter



855C7150-A53D-4E6E-BE22-4734B4DF5A89.jpeg
 