Hey y’all. Quick question about the overload protection on a 802. How does it work and when?

I’ve overloaded my machine several times to the point when it bogs down and the frequency gets really low, the machine is sputtering and puffing smoke. It has never tripped the overload.


Sent from my iPhone using Tapatalk
 

justicelee26

Member
41
4
8
Location
South Carolina
Hi. There is a recent thread discussing the same thing with the MEP 803a. This is common among all of these machines. My 803a will drop frequency and blow black smoke if loaded way beyond capacity but it take a lot to trip the breaker. If you are using the machine to power your house you can always use a breaker in your main panel to limit current output from the generator coming into the panel. I actually like that the breaker doesn’t trip easily. It allows you to start very large inductive loads with really high starting current. For example your 802 should be able to start a decent size central AC unit. Hope this helps. If you have any more questions feel free to ask.
 

fa35jsf

Active member
135
35
28
Location
OKC, OK
Unfortunately mine won’t start my ac unit, but it’s also a 4 ton unit from the 90’s so yeah...

And I just read that post after making this one. So it can take minutes to trip? That’s probably fine for military equipment but I’m concerned about sensitive home electronics drying due to low frequency or voltage.


Sent from my iPhone using Tapatalk
 

justicelee26

Member
41
4
8
Location
South Carolina
The overload trip is a function of both time and current. The more load you draw the more quickly it will trip. It is designed to trip to protect the generator not the loads. Again, a breaker in your main panel can give you a faster trip. If you only use the generator for backup power you can manage loads by opening the breakers for large loads that you don’t want to start without turning other loads off first. For example, the 802 won’t run an electric water heater with a lot of other things running in the house so you can open that breaker to prevent that load from getting dropped on the generator. If you need the hot water you can turn off other loads then shut the water heater breaker. That way there is never a chance that you will overload the generator. If you are still worried about sensitive electronics you could get a UPS to protect them. That will help with abnormalities in ulitity power as well. Also I have noticed when putting very large loads on my 803a that voltage almost never drops out for more than a fraction of a second but frequency will drop a lot. A lot of electronics (not all) can run fine as low as 50 hz because that is the standard frequency in some countries.
 