Power Cable Question

storeman

Well-known member
1,345
52
48
Location
Mathews County, VA
Fellas,
Two weeks ago I bid on a GL auction of contractor materials being disposed of on completion of the Tyson's Corner, VA and Dulles Airport Metro subway extension projects. Construction is complete and the Metro system is testing now.

Won a lot of heavy industrial items, such as 2/4/800 and 1200amp breakers that I am listing on the big auction site.

There was a power cable in one of the lots which I hoped was #4 or #6 to redo my house hook up. I did not preview the auction. Cable turned out to be 60' and 10' pieces of a cable called Portable Power Cable, 2000 volt dry, 1000 volt wet, size is 3/C #2AWG. Connectors can be put into perspective by my size 12 shoe.

Question is what generator would this cable be appropriate for? I guess I could install it as way overkill for a 10KW but don't know if it could be direct buried or put in 2" conduit. Thoughts?

Jerry

IMG_2104.JPGIMG_2103.jpgIMG_2100.jpgIMG_2101.jpg
 
Last edited:

storeman

Well-known member
1,345
52
48
Location
Mathews County, VA
I'm assuming you can't have too big a conductor. Now to figure out how and whether to install it or sell it. #4 or #6 would meet my needs.
 

Jimc

Member
725
1
18
Location
Mullica, nj
#6 is more than enough for a short run from an 003. no you cant have too big a conductor. the #2 will work fine also. decisions decisions
 

Triple Jim

Well-known member
1,376
291
83
Location
North Carolina
#2 isn't ridiculously large. Every three numbers doubles current carrying capacity, so #2 is not even double #4, and is slightly more than double #6. I'd probably keep it and use it.
 

s011883

Member
39
2
6
Location
Hartford MI
I use 120' # 4 SO cord to run my 003 generator at my house. I went with the #4 for voltage drop and so I could keep the generator 100' from the house. Those connectors that came with your cable cost big $$.
 