Safest way to uses a MEP 804b as a backup generator

jarmagno

New member
1
0
1
Location
lake zurich IL
This is my first post on a forum....
What is the safest way to use a MEP 804b as a whole house generator? I have seen the Generlink transfer switches, which allow the main panel to remain as is, but they don't work with 3 phase generators. What are people using?
Joe
 

DieselAddict

Well-known member
Steel Soldiers Supporter
2,543
2,093
113
Location
Efland, NC
The safest way is to use a double ended transfer switch. That makes sure you can't export power to the grid while you are on generator power.

Since the 804 is a 3 phase only generator you'll be limited to 2/3rds capacity max.
 

DieselAddict

Well-known member
Steel Soldiers Supporter
2,543
2,093
113
Location
Efland, NC
That has been discussed a number of times. The short version is - If you are doing backup emergency power don't worry about it. You aren't going to run the unit long enough to matter.

BUT - If you are off grid its not the right generator for the job. BUT BUT if you are off grid why not wire your setup for 3 phase, then its the right generator. ;)
 

Guyfang

Moderator
Staff member
Moderator
16,924
24,545
113
Location
Burgkunstadt, Germany
Chris, could not have said it better. The world will NOT end if you run an unbalanced load for a week or two, or even longer. All year long? then get the house set up for 3 phase power and be done with it.
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,861
6,075
113
Location
MA
Good point on the duration of run. I have stayed away from the 804s because I didn't see much value to the homeowner/small business segment (all single phase requirement). Maybe I should reconsider, with the caveat known.
 

Suprman

Well-known member
Supporting Vendor
6,862
697
113
Location
Stratford/Connecticut
I have seen it done and it does work. But you only have around 2/3 capacity of the generator. So you are back to running a 10k basically, just with a higher fuel draw.
 

Guyfang

Moderator
Staff member
Moderator
16,924
24,545
113
Location
Burgkunstadt, Germany
I have seen it done and it does work. But you only have around 2/3 capacity of the generator. So you are back to running a 10k basically, just with a higher fuel draw.
It would be interesting, when you have a 3 phase setup. Or a house, barn, shop and that kind of thing.
 

Triple Jim

Well-known member
1,376
293
83
Location
North Carolina
It's possible to use one or more transformers to convert from three phase to single phase. You can find a lot of information about it with a search for "three phase to single phase transformer" or something similar.

But I would think that the 804 would be more than adequate for a whole house when using only 2/3 of it, unless you have a lot of electric heating requirements.
 

98G

Former SSG
Steel Soldiers Supporter
6,089
4,493
113
Location
AZ/KS/MO/OK/NM/NE, varies by the day...
It's possible to use one or more transformers to convert from three phase to single phase. You can find a lot of information about it with a search for "three phase to single phase transformer" or something similar.

But I would think that the 804 would be more than adequate for a whole house when using only 2/3 of it, unless you have a lot of electric heating requirements.
The phase converters cost almost as much as the generator.

Agreed that 2/3 of an MEP804 is plenty for a house. The difference in fuel consumption compared to an 803 is the issue. For occasional use, I don't think it is a big deal.
 

CMPPhil

Well-known member
536
376
63
Location
Temple, NH
Hi

Question, will 220 volt motors be happy running on 2 legs of 3 phase? I'm thinking of well pumps.

Cheers Phil
 

155mm

Chief and Indian
Steel Soldiers Supporter
1,181
397
83
Location
Guymon, OK
The safest way is to use a double ended transfer switch. That makes sure you can't export power to the grid while you are on generator power.

Since the 804 is a 3 phase only generator you'll be limited to 2/3rds capacity max.
IMG_2007[1].jpgIMG_2008[1].jpg

This is the switch Chris was refering to, you can see the load (house) is the center poles, the bottom post (power company), top posts (generator). With this switch there is no way to get power from the genny to line, unless there is major ground issues.

If you have not read this thread, would be good reading.

https://www.steelsoldiers.com/showthread.php?167498-Wife-is-now-a-green-iron-believer/page2

Also grounding grounding grounding, proper grounding is something that I have seen alot of times overlooked, dont know, or just lazy. Grounding is the safety that keeps the angry pixies from going thru you to the ground if something goes wrong.
 

155mm

Chief and Indian
Steel Soldiers Supporter
1,181
397
83
Location
Guymon, OK
Hi

Question, will 220 volt motors be happy running on 2 legs of 3 phase? I'm thinking of well pumps.

Cheers Phil
I have had no issues running 208 to a 240v water well, BUT it is a gamble. Our water well repair shop says the well motors are rated 240 +/- 10% for warranty issues, so 208 is outside the 10% but just a little bit for warranty. How would warranty know the difference between a brown out and 208 from a genny? unknown, except for honesty.
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,861
6,075
113
Location
MA
Yeah most devices unless specifically listing auto switching voltage (100-240 (50/60hz) are only good for a +/-10% swing.
 

LEOK

Active member
125
26
28
Location
Gainesville/Fl
Since this is turbo unit It will be interesting to see, let's say the average load works out at 7k will there really be a big difference?

The phase converters cost almost as much as the generator.

Agreed that 2/3 of an MEP804 is plenty for a house. The difference in fuel consumption compared to an 803 is the issue. For occasional use, I don't think it is a big deal.
 