Voltage Problem MEP-002

mtfleming

Member
68
16
8
Location
bristol, tn
Have a MEP -002. When it's running with a small load (500W), it works fine. voltage is fully adjustable. When I then add a load up to say 50%, the voltage drops to 200V (from 240V), and is no longer adjustable. What could this be? Thanks to all in advance for your help!
 

Triple Jim

Well-known member
1,373
277
83
Location
North Carolina
It's likely that for some reason you don't have enough exciter field current. It could be a lot of things. I'd start with checking the diodes on the A4 board (in box under output lugs). If they're OK, I'd check the resistances of the windings of CVT1 against the resistances in the -34 manual. If those check out OK you should probably check the rotating diodes in the generator.

There are some troubleshooting procedures that can be very helpful in the manual too.
 

jamawieb

Well-known member
1,413
514
113
Location
Ripley/TN
More than likely the voltage regulator. There are 2 adjustable pods on the voltage regulator R16 and R15 (I think), use a very small flat head screw driver and make 1 full rotation, then move it back to the original position. See if that helps.
 

Guyfang

Moderator
Staff member
Moderator
15,981
22,378
113
Location
Burgkunstadt, Germany
While you are looking at things in the AC output box, look for loose wires and broken wires. Look at the solder joints on the A4 card.
 