voltage testing info needed

shootist

Member
182
0
16
Location
RI
I've searched and read and read maybe I'm missing it.aua

Can someone tell me how to test the voltage at or leaving the generator ,
then leaving (or at) the regulator?
Just not sure where to place the probes. Don't have the military test kit I'm using a standard digital volt meter.
Also should either be low- how do I adjust? let me re-word that -I know how to adjust the Gen.from what I read, but i've read the regulator can be adjusted also.
 

shootist

Member
182
0
16
Location
RI
Thanks for reply 70Duece.
I will try that.
but that method generates another question:
When I removed the positive terminal at the battery(s)
the truck shut down.
So if I remove the output cannon plug to test wont this essentially
cause a shutdown also?
or can I just probe one of the wires?
also you mentioned put the negative probe on the box
I'm guessing one of the ground straps would be ok?
 

cranetruck

Moderator
Super Moderator
Steel Soldiers Supporter
10,350
75
48
Location
Meadows of Dan, Virginia
To measure a voltage, you don't need to disconnect anything. There is a voltage drop across the regulator of perhaps 2 volts (internal SCR) and you need to have the battery connected.
For access to all check points, remove the cover of the regulator.
 