I'll stick with kw since it is a unit of power.forget kw compare amps
Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!
I'll stick with kw since it is a unit of power.forget kw compare amps
Ike,Isaac-1 said:Speddmon, this may be getting a bit off topic, but Onan did make a 3.5 inch bore J series diesel engine in their civilian models, the 17.5RDJF, the big difference between this and the MEP-003a engine is the RDJF is a water cooled block.
Ike
Speddmon I would like you to try spell this out for me please I will tell anyone I don't know it all but I don't get itThe military took into account the .80 (80%) power factor rating, that's why the set is rated for 10KW at 80% PF. The TM states "A 0.8 power factor load equals a 100% meter reading for maximum rated load. A 1.0 power factor load equals a 80% meter reading for maximum rated load"
I am talking about when comparing the military gen sets to the civilian ones they don't lie as bad about the amps that a civilian one can handle as they do kw. Also most homes use 220 so if you know what your house max amp draw is you can match that to the gen set you need without having to figure watts.I'll stick with kw since it is a unit of power.
Sorry, I just can't make myself do it......I may need to be tied down and restrained.....maybe a little elctro-shock therapy..I am talking about when comparing the military gen sets to the civilian ones they don't lie as bad about the amps that a civilian one can handle as they do kw. Also most homes use 220 so if you know what your house max amp draw is you can match that to the gen set you need without having to figure watts.
amps x volts= watts
Speddmon I would like you to try spell this out for me please I will tell anyone I don't know it all but I don't get it
I'm not into the civilian generators as much as I am the military ones, so if there is a discrepancy in the amp ratings of the two, it would be because of the power factor correction as I stated above. It's quite possible that if you had a 10 KW civilian set the amp rating should be lower than the military set, because they would not take into account the power factor...example; a 10 KW civilian might look like this...(41.66 amps x 240 volts) / 1000 = 10KW.rat4spd said:Sorry, I just can't make myself do it......I may need to be tied down and restrained.....maybe a little elctro-shock therapy..Csm Davis said:I am talking about when comparing the military gen sets to the civilian ones they don't lie as bad about the amps that a civilian one can handle as they do kw. Also most homes use 220 so if you know what your house max amp draw is you can match that to the gen set you need without having to figure watts.
amps x volts= watts
Maybe Speddmon can help me, but I think I'm hopeless.
Sorry, I was just trying to clear up the differences in why the sets are rated why they are...honest! But the power triangle is why I didn't get out the old books and start reading about it again for the post...I was going by memory. I didn't like it the first time around when I had to learn it, and I sure don't want to have to go through it again.
I'm more of a hands on kind of guy, the theory stuff is interesting, but I like to get dirty and see sparks!!!
Anybody who want's to debate apparent vs real power, power factor correction and why it's important and all of that good stuff, I'll send them your way ...or they can take a couple of years of correspondence classes and learn it the "fun"way
I have a Generac GP7500E and it is no quieter than the MEP-002a I bought. I was thinking of buying an ASK for my MEP-002a. Have you done a test with an MEP-002a and an ASK?I realize this is an old thread, but I just did a blog post regarding noise levels for the MEP-002A and MEP-003A units. The bottom line is that they are about the same noise level as Honda's best and largest worksite generator. This is without the ASK. The O02A is 2 dbA louder than the 003A. Tuning your unit and ensuring it is tuned properly with the injection pump is key. Ensuring there are no loose parts on the unit is also key...One little rattle can drive you crazy... So military units are not any louder than similar gas units -- even good ones. I completely disagree about store-bought sound attenuation features. They are very expensive and much higher than a $200-300 feature. Building a simple plywood cabin around your MEP is easy and cheap and does a great deal to deaden the sound and direct it away from your home/building. Just ensure proper and generous cross-ventilation in the units as they are air cooled...Here is my post on how loud MEP-002A and MEP-003A units are compared to lots of other noises and Generac and Hondas... My bottom line is that the noise levels of military units is the SAME as civilian units and is waaay over blown....
The specs that I made about MEP002A and MEP003A were directly from a military manual, namely: MEP-Various-Handbook-for-Mobile-Electric-Power-Engine-Generator-Standard-Family-General-Characteristics-MIL-HDBK-633/.I have a Generac GP7500E and it is no quieter than the MEP-002a I bought. I was thinking of buying an ASK for my MEP-002a. Have you done a test with an MEP-002a and an ASK?