- 540
- 22
- 18
- Greenville SC
Starting a new thread on the generator modification to the air input and exhaust. Got the exhaust hood built today and will put up a few pictures.
Can you maybe post a link here?Starting a new thread on the generator modification to the air input and exhaust. Got the exhaust hood built today and will put up a few pictures.
Be sure to read up on the code for generators in your area. If you are using an ATS the rules are different concerning connected load. You aren't allowed to automatically attach more connected load than your generator can handle. If you have a 5kw genset then you can't put more than 5kw of connected load to your generator subpanel/ATS setup.Well, finally got through all 23 pages. Looks like a great install. Looks like you have yours wired in before it hits the main panel. Any issues with the generator not being rated to supply the entire load of the panel? I'm probably going to hard wire my 802 into an ATS before the panel so as not to have to move circuits to a separate sub panel and use then use some load shed relays to make sure the high wattage devices don't come on together.
I saw a note in the product literature for the ATS I'm looking to use stating that, but wasn't sure if it was more of a guide line. I can see where the issues come into play obviously but it seems if you do it right it can be managed.Be sure to read up on the code for generators in your area. If you are using an ATS the rules are different concerning connected load. You aren't allowed to automatically attach more connected load than your generator can handle. If you have a 5kw genset then you can't put more than 5kw of connected load to your generator subpanel/ATS setup.
Unless your ATS has load shedding. APC's transfer switches did this. Only consumer one I saw that did. Think they got discontinued.Be sure to read up on the code for generators in your area. If you are using an ATS the rules are different concerning connected load. You aren't allowed to automatically attach more connected load than your generator can handle. If you have a 5kw genset then you can't put more than 5kw of connected load to your generator subpanel/ATS setup.
Howdy,I have debated on stepping up to a 15kw unit but can't justify it because my 10kw unit does everything I need it to do.
Not trying to argue the logic of the ATS code but more so the manual as well. Sure its assumed you manual manage the load, but how do you know that the HW isn't running, or your aux heat isn't running when you flip the switch? Not saying you in particular, just in general. Unless there's a checklist sheet next to the switch whats to stop someone not trained on the system (father in law watching the house for example) from throwing the switch and connecting more than than the gen can handle.Not overloading a generator with an ATS is not a guideline. If you use an ATS you MUST have AUTOMATIC load shedding as to not create an overload on the generator. If you do and its a permitted job its a guaranteed fail from the inspector.
If you have a MTS then it is assumed that the load management is also manual. If it is AUTO then its assumed that the load management is AUTOMATIC.
With an 802, you can only put 5kw of connected load on it with an ATS or it will be a guaranteed fail from the inspector.
Thanks. I figured thats what you did put couldn't quite tell.I have an 803a, that's what is pictured in my install. I rarely have to manually manage loads. I just know that I can't run the strip heat on the heat pump, water heater, and other high resistive loads at once. I have ran my oven, clothes dryer, and central A/C as well as other normal incidental loads such as various lights, tv's, computers, etc. at once. I have ran my unit at 130% load. I have tested it to produce 14kw for nearly 20 minutes before tripping an overload switch.
These are good units. Anyone who tells you differently doesn't know them. I have seen units with 7000 hours on them and my buddy worked on one with nearly 10,000 hours on it over in the desert. These things are built for the harshest environments. A little GA sun is no comparison to the deserts in Iraq and Kuwait.
I ran a short stub of conduit into the generator from the "L" connector. I also drilled two holes and screwed the high voltage door shut. I have a 7 year old boy and wanted to make sure his curiosity didn't get the best of him. Also for those not familiar with these sets, it is for their safety as well.
It's like umbrellas, Glockfan. I don't know if there is any science to it or anything, but:Having done all this, I have been without power for about 8 hours in two years! Go figure...
My solution for my "manual interlock" is to pin a verified checklist written in an EASY to understand procedure next to the breaker box and on the generator itself (in gallon size Ziplocs). In addition, I have a green dot (used green sharpie pen) next to every breaker that needs to get thrown to on position (one at a time) so life is pretty much normal during an outage. This way all the wife, or trained house sitter, has to do is follow the procedure as written. It even helps me to not have to think about which breakers need to be thrown when a power event occurs. If its storming and dark, looking for a green dot with flashlight in hand is easier than trying to read breaker labels in dim light ( o well pump, etc...) vs not thrown (hot-tub...) You could even use some color coded vinyl dots with legend: green = always on, yellow = only when necessary, red = always off except when on utility pwr.Not trying to argue the logic of the ATS code but more so the manual as well. Sure its assumed you manual manage the load, but how do you know that the HW isn't running, or your aux heat isn't running when you flip the switch? Not saying you in particular, just in general. Unless there's a checklist sheet next to the switch whats to stop someone not trained on the system (father in law watching the house for example) from throwing the switch and connecting more than than the gen can handle. .
I just want to take a moment to point out how awesome you are for going through this effortMy solution for my "manual interlock" is to pin a verified checklist written in an EASY to understand procedure next to the breaker box and on the generator itself (in gallon size Ziplocs)...
Are you connecting an MEP or a commercial genset to your house? If you are going to use an MEP, the connection should be made at the terminal lugs on the generator.
You should leave your ground bonded to neutral via the copper bar while your MEP is "portable". You will notice that my bar has been removed since I'm perm connected.
Glad to help!Just note that that this pick and the bonding note helped me out today, leaving it portable I'm leaving the bar in place.