    MEP006A

    I have the other A11 from my other gen, I am sending the new VR back to where I bought it for replacement. What senses the voltage and sends the signal to the Tac relay, could any of that circuit be bad?
  2. B

    MEP006A

    Fat fingers 208/120 I am measuring 208/120
  3. B

    MEP006A

    298/120
  4. B

    MEP006A

    the over voltage light
  5. B

    MEP006A

    I am not sure what is happening to my replies, because I don't see them here. I changed the VR in the A11 and when I started the unit up the freq and voltage gage went full dial then to nothing, I put the original VR back in the A11 and I am back to good voltages and freq but only in Battle...
  6. B

    MEP006A

    I changed the V Reg and now I have nothing, dials go freq and vol go up and then they go down, I put the original VR in and I am back to voltages and freq ok, but have over voltage light on and have to run in Battle Short
  7. B

    MEP006A

    I did do that, and nothing. I put the new Watt Transducer in and a new A11 excitation box I bought in and fired it up and meters moved, but it would not stay running unless I put on the Battle Short. So with the battle short on I dialed in the voltage to 208/120 but the frequency would not go...
  8. B

    MEP006A

    on the metal can relays (k5, k6 etc.) I don't see any labeling, but I do see a pin that is different is that pin to be on the top or bottom when installing?
  9. B

    MEP006A

    I did do that, and nothing. I put the new Watt Transducer in and a new A11 excitation box I bought in and fired it up and meters moved, but it would not stay running unless I put on the Battle Short. So with the battle short on I dialed in the voltage to 208/120 but the frequency would not go...
  10. B

    MEP006A

    after replacing the watt transducer I have voltage I measure 208 between phases and 129 to ground with both the onboard measuring and my fluke meter, but it will only run in battle mode due to an over voltage fault. any ideas?
  11. B

    MEP006A

    I will look tomorrow, any Ideas on the voltage of my other gen?
  12. B

    MEP006A

    I put the exciter back in the other Gen and it worked, in doing my voltage measurements on the three phases I noticed that the working gen measuring from phase to phase I have 240-253 depending on what I set the VAR at and I have 138 to ground from each phase. but on the AVSS not all the...
  13. B

    MEP006A

    I am looking at the TM's I can not find these to trace. Can you tell what page and what TM it would be on?
  14. B

    MEP006A

    Will an exciter fo a MEP006 precision work in mine?
  15. B

    MEP006A

    I will do that tomorrow when it is not raining and post results
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks