- 16,923
- 24,544
- 113
- Location
- Burgkunstadt, Germany
Has anyone here considered that there may be a step down transformer for the computer? I would hook it up and run it. The company told you you can, so go for it. Yes, you can change the startup voltage. BUT, no one can tell you how. Its not something anyone would have to do in the Army, so there was no reason to put it in the TM's. The gen set is a worker, you will get good service from it. BUT, if the components in the control cube go tits up, that can be a problem. The only thing I would warn you about is phasing. Make sure your set is putting out the same as your equipment needs. easy to change, but better to test first. Most things have a phase protection circuit to prevent machines from running backwards, but not all. I have seen many very large messes when equipment ran backwards. The reason I say test, is that someone along the way may have mixed up two phase wires. Voltage reads normal. But phase is out. the place this normally happens is on the K1. the input wire get mixed up on the input side, the out put side and at the load terminals. This happens very often.