I'm not getting readings from the lugs, got readings from the convenience outlets. Am I doing something wrong? Where should I start looking? Thanks
 

ufc702

New member
14
0
0
Location
Wahiawa, HI.
So far I pulled the panels tested K1 and got power at C1, B1, A1 but nothing at A2, B2, C2 I also don't have readings off of X, Y, 11, & 12 where should I be looking at? Tested the relays they seem to be good.
 

Guyfang

Moderator
Staff member
Moderator
18,086
27,145
113
Location
Burgkunstadt, Germany
Look at the schematics. What tells K-1 to close? When you push up S-5, (A.C. circuit interrupter) whats suposed to happen? You should get a signal at K-1, terminal Y, or X, can't remember and am not at my computer so I can not look. But in any case, one of the wires should have 24 volts. If not, go from there. Its not hard, take it one thing at a time. Trace it back to the S-5. You can also follow the trouble shooting diagram in the book. Its well written for this problem. It explains how to test the K-1 also. Easy and you don't even have to remove it or have the set running.
 

ufc702

New member
14
0
0
Location
Wahiawa, HI.
Look at the schematics. What tells K-1 to close? When you push up S-5, (A.C. circuit interrupter) whats suposed to happen? You should get a signal at K-1, terminal Y, or X, can't remember and am not at my computer so I can not look. But in any case, one of the wires should have 24 volts. If not, go from there. Its not hard, take it one thing at a time. Trace it back to the S-5. You can also follow the trouble shooting diagram in the book. Its well written for this problem. It explains how to test the K-1 also. Easy and you don't even have to remove it or have the set running.
Been busy with work, gonna get back to it sometime next week, will log my progress. Thank You Guyfang!
 

ufc702

New member
14
0
0
Location
Wahiawa, HI.
Look at the schematics. What tells K-1 to close? When you push up S-5, (A.C. circuit interrupter) whats suposed to happen? You should get a signal at K-1, terminal Y, or X, can't remember and am not at my computer so I can not look. But in any case, one of the wires should have 24 volts. If not, go from there. Its not hard, take it one thing at a time. Trace it back to the S-5. You can also follow the trouble shooting diagram in the book. Its well written for this problem. It explains how to test the K-1 also. Easy and you don't even have to remove it or have the set running.
ok so I was able to get to it today, After reading the TM I discovered that I never pushed up S-5 to send the signal to K1 so once I did that got readings instantly. Going to go over the gen more during the week as time permits but I want to get this dialed in, I enjoy learning how this thing works and discovering issues and working them out
 

ufc702

New member
14
0
0
Location
Wahiawa, HI.
Ah, good old S-5. You will never forget that in you next 60 years.
You got that right!

Ok so everything is running smoothly and working like it should. I'm thinking of picking one up for a jobsite on another island and I was looking at the trailer mounted units, anything I should be looking out for on both the generator and the trailer?
 

Daybreak

2 Star Admiral
1,522
775
113
Location
Va
You got that right!

Ok so everything is running smoothly and working like it should. I'm thinking of picking one up for a jobsite on another island and I was looking at the trailer mounted units, anything I should be looking out for on both the generator and the trailer?
Howdy,