• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

 

Cable size for Mep002a

RJM27

Active member
Steel Soldiers Supporter
359
26
28
Location
Burdett NY
What are the suggestions for Cable size and configuration to come off the lugs on my Mep002a. My store bought Gen set has 220volt twist lock that goes to outlet, then through transfer switch (sorta home made but does work well). Any experince would be appreciated.
Thanks Bob.
 

jbk

Member
404
5
16
Location
livingston la.
your gen. is 26 amps. at 240. most use 10/4 which is good for 30 amp. 240 up to 100 ft. i use 8/4 good for 35 amp. it still fits in the L14 twist lock conn. and is good for 35 amps. at 100 ft.
 

RJM27

Active member
Steel Soldiers Supporter
359
26
28
Location
Burdett NY
Ok here are pics of what I'm using w/ package store genset, it is an L14 twist i put on it and same with outlet installed. Suggestions on hooking to Mep002a; If i want to go 100' what type cable is the best and were to get it. Assume I should wire dirrect to lugs, will the 30amp outlet I have be sufficient. I can change the whole set up. My existing cord is only 25'
Thanks Bob.
 

Attachments

jbk

Member
404
5
16
Location
livingston la.
you can use your existing wire/conn. if you want, i cant tell what gauge it is. i use 8/4 4/c 600 volt water resistant wire its a little heaver than the 10/4 which is all you need. the conn. method is on the data plate on the conn. box. the wire can be had almost anywhere, home depot, ebay or elec. supply. 30 amp. is all it will do. if that is a backfeed method you might consider a transfer switch.
 

steelandcanvas

Well-known member
6,187
85
48
Location
Southwestern Idaho
A transfer switch is not just a consideration, it's required by law. You certainly don't want to start your genset and fry some poor unsuspecting lineman trying to restore your outage. Transfer switches are expensive, however there is an alternative. Interlock switches do the same thing, and are fairly inexpensive when compared to transfer switches. They are designed, when installed correctly, to prohibit you from closing the main breaker and the genset breaker at the same time. Here are a couple of distributors:
Generator InterLock Kit - How do I connect my Generator Breaker to my Generator
Panel Interlock Kits
Please do not hook up your genset without something to disconnect you from the utility.
 

RJM27

Active member
Steel Soldiers Supporter
359
26
28
Location
Burdett NY
Hey gus I have the interlock switch installed on my sub pannel box (200amp), I agree that is the bare minimum, hopefully someday I can get the transfer switch, keep waiting for a sale. What do you guys think about diirect connect to the Lugs w/sjt cord, or go with a disconnect and outlet?:roll:
 

steelandcanvas

Well-known member
6,187
85
48
Location
Southwestern Idaho
What do you guys think about diirect connect to the Lugs w/sjt cord, or go with a disconnect and outlet?:roll:
If you don't plan on using the genset for anything but your house back-up, just attach to the lugs. I came off my lugs with a junction box and placed a 125/250V 50A Female Twist-lock Receptacle on it. With a male/female cord set-up, I can plug from the genset directly into my shop for back-up power, or to a scatter (spider) box with multiple 240V and 120V receptacles on it. With a male/pig-tail cord, I can attach to any panelboard that needs temporary power. This design makes my genset very versatile. BTW, I went with the 50A rating as I have an MEP-003A.
 

derf

Member
926
13
18
Location
LA
Your yellow wire is DANGEROUS. You should have a male connector on the gen end and a FEMALE connector on the other end and a corresponding male receptacle for the FEMALE connector.
What you have now is a potential shock hazard if plugged into a running generator and not plugged into the box on the other end,
i.e. you have 220V exposed.
 

Attachments

Last edited:

steelandcanvas

Well-known member
6,187
85
48
Location
Southwestern Idaho
Your yellow wire is DANGEROUS. You should have a male connector on the gen end and a FEMALE connector on the other end and a corresponding male receptacle for the FEMALE connector.
What you have now is a potential shock hazard if plugged into a running generator and not plugged into the box on the other end,
i.e. you have 220V exposed.
WOW! Good catch, I hadn't noticed that. That needs to be corrected ASAP!
 

jbk

Member
404
5
16
Location
livingston la.
i didnt even notice, but if you have an interlock on your sub panel you should have a gen. inlet box which will have male prongs and a female L14 from your gen.
 

steelandcanvas

Well-known member
6,187
85
48
Location
Southwestern Idaho
I'll try and post some photos tonight of my set-up, hopefully that will clear everything up for Bob. (RJM27) He's got a potentially dangerous situation (male/male on a cord) that needs to be corrected.
 

RJM27

Active member
Steel Soldiers Supporter
359
26
28
Location
Burdett NY
The set up was put together to get me going during a extended power outage, I understand the risk of shock and would not fire the generator until the plug was installed. The lock out is inside the disconect pannel, mechanical device between the 30amp breaker and 200 amp service breaker, gen power cannot get into pannel unless main is off. I'm in the process of changing this set up, that's why I'm looking for input. We have had several power outages(squirles & racoon's, so they say, even heavy winds seem's to knock us out), over the last couple of years that have lasted for long periods, the gas powered gen set is underrated and screams. I like the thought of a disconect on the genset trailer, which would give more flexability. Hey guys I really appreciate all the comments and help, you guys got it together and it is more help then you realize.
Thanks Bob.
 

derf

Member
926
13
18
Location
LA
If I were you I would either spend the extra bucks to make that yellow wire more properly safe or hard wire the box end and leave the gen end like it is.
Be careful going to automatic transfer switches. It sounds like you have a good switch/disconnect in place. Oftentimes if you go auto you have codes and bureaucracies to deal with.

Codes and inspections/inspectors aren't bad things, but sometimes they just lack common sense.
 

RJM27

Active member
Steel Soldiers Supporter
359
26
28
Location
Burdett NY
I'm without a doubt changing the cord, that was my original question on cord size and length, would like to go 100'. I got a PM on Ronk transfer switches, would like to keep everything outside, that is why I have a 200amp exterior entrance box. Next questions will be proper way to hook to the lugs and if I'm going through a sub panel. Thanks again Bob.
 

jbk

Member
404
5
16
Location
livingston la.
connect lugs L1 and L3 for your hots and lo for your neutral in the box. be sure the reconnect switch is set on 120/240 single phase. remove the neutral ground bond at the generator after you connect to the house.
 

reset2

Active member
166
60
28
Location
Myersville MD
Referring to post #8. The pictures in the post.

All right I have to ask. Just getting into this military stuff more and more. In your picture of the MEP on the little HF trailer can I ask what paint you used to paint the genset? I will be going to the Expo in May at Ripkin field and I should be able to find a paint seller there just wanted to know what to ask for (year or vehicle used on originally). Thanks.
Second question the switch box on the third picture (on the fender). What is this box? Did it come on the trailer originally or did you find it somewhere? Thanks again
Reset2
 
Last edited:

Chrispyny

Member
294
12
18
Location
NY
Referring to post #8. The pictures in the post.

All right I have to ask. Just getting into this military stuff more and more. In your picture of the MEP on the little HF trailer can I ask what paint you used to paint the genset? I will be going to the Expo in May at Ripkin field and I should be able to find a paint seller there just wanted to know what to ask for (year or vehicle used on originally). Thanks.
Second question the switch box on the third picture (on the fender). What is this box? Did it come on the trailer originally or did you find it somewhere? Thanks again
Reset2
Ditto on both paint and switch box please...
 

jbk

Member
404
5
16
Location
livingston la.
the paint is ppg automotive. the fella at the paint store shot the color from inside a piece of sheet metal from a 002 kinda a dark forest green color. kinda a simi flat cures very fast. ive used this paint on all my gens. more examples of this paint can be seen in my album under my profile here, $40.00 a gal.. the decals were made at a local sign co. the switch box on the 1.5 trailer is original to it allowing you to switch from one set to the other.
 
Last edited:
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks