Ok so tomorrow I'm going to try taking it apart and doing the fuel lines. Any pointers for them? How do I get them all off? And anything I should do in addition? I have the fuel tank nuts but seeing as I just put 3 gallons in I don't want to pull the tank if I don't have to :) Diesel is expensive! I will figure it out but thought I should ask!
Even if that gets wasted, it's better than a full tank (or more if AUX is being used) being wasted when the existing one leaks the first time you run it overnight & it decides to spew. Then you are out the fuel & power. Changing them out is not fun no matter the route you go, but making sure it is done right, you won't even need to worry about it leaking again.
 

2Pbfeet

Well-known member
563
1,085
93
Location
Mt. Hamilton, CA
Ok so tomorrow I'm going to try taking it apart and doing the fuel lines. Any pointers for them? How do I get them all off? And anything I should do in addition? I have the fuel tank nuts but seeing as I just put 3 gallons in I don't want to pull the tank if I don't have to :) Diesel is expensive! I will figure it out but thought I should ask!
Better to drain the tank now when you have time and control, than later when you might not. I would suggest that as this generator is new to you, while you are changing the tank nuts, check for debris, slime, and crud in the tank, and wipe the inside clean. No sense in washing crud into your filters or worse.

There are several threads here that cover changing the fuel lines, but in general, they are just fuel lines.

All the best,

2Pbfeet
 

pstansel74

Member
47
91
18
Location
Tolland, CT
So I got it disassembled it except the fuel lines. They scare me a little. @CallMeColt do I need a heat gun or do I just pull the tubes off and on? The petcock worked great. The bolts to get the muffler off were a PITA though!
 

CallMeColt

Well-known member
Supporting Vendor
1,089
1,620
113
Location
Wilson County, Texas
So I got it disassembled it except the fuel lines. They scare me a little. @CallMeColt do I need a heat gun or do I just pull the tubes off and on? The petcock worked great. The bolts to get the muffler off were a PITA though!
Pull, yank, cut. Doesn't matter. They're designed to bond after some head cycles to seal well. It's why those plastic tees are a throw away item in my opinion.
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,941
6,356
113
Location
MA
On return lines, I use zip ties at each line end. On the main lines to the metering pumps, you can use hose clamps effectively. Just find some 1/4" - 7/8" hose clamps, most auto parts stores, ag supply stores with bolt bins, etc will have hose clamps. You may be able to reuse the compression fittings for the pump side, and only use a hose clamp at the top feed side where the line interfaces with the rigid fuel delivery line.
 

CallMeColt

Well-known member
Supporting Vendor
1,089
1,620
113
Location
Wilson County, Texas
What size hose clamps do you use? I am having trouble finding 1/8inch.
None are needed with the OEM line as it is return line, not feed line. It will "bond" after a heat cycle or two & seal up. For piece of mind, a zip tie will do but again, not needed. It's why they're hard to pull off after they have been on. If you are using something else, get something that is the right OD for that fuel line, just don't over tighten. These don't get more than 10ish psi.
 

pstansel74

Member
47
91
18
Location
Tolland, CT
So I buttoned it back up... then decided to test it. Sigh. Everything works great at the panel once I replaced the fuel gauge but I have no power out. Took a deep breath and walked away for a bit. I tried flipping the interrupt switch before anyone asks :) I will get my voltmeter out and test it more fully but the convenience outlets at least were dead. I reaaally was afraid of the wires!
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,941
6,356
113
Location
MA
What setting do you have the voltage/phase selection switch set to behind the gauge panel? And does your hertz gauge register? How about the voltage gauge... showing any voltage? Where is your AM/VM switch set on the gauge panel?

The convenience outlet has a resettable breaker on it as well.. tell us what the gauges show, if anything.
 

pstansel74

Member
47
91
18
Location
Tolland, CT
It is 120/240 1ph behind the panel. L3-L1 1 phase on the front. Gauge shows 220. 60hz on the other gauge. Nothing showing for the percent rated current.

I tried the various resets on the panel and didn't see anything but I didn't find one specific to the convenience outlets. Guess I need to look in the manual a bit.
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,941
6,356
113
Location
MA
The PRC gauge should be registering zero if power is not leaving the machine. Your machine IS generating power though, so breathe easy there. The trick is to now get it out of the machine.

When you engage the circuit interrupt switch on the gauge panel, does the green bulb light up?
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,941
6,356
113
Location
MA
Getting warmer... I think you are going to end up pulling the cover over the gauges and cleaning the AC contactor box, which resides behind the wall with the S8 switch. That box, when voltage is applied, is what transfers power down to the lugs. Its known to get hung up by corrosion.
 

Guyfang

Moderator
Staff member
Moderator
17,198
25,437
113
Location
Burgkunstadt, Germany
Start with the easy stuff. Reset the 120 volt convenience outlets. Read the book a little more.

If the DS7, (ACV output light) comes on, then the K1, (AC circuit interrupter relay) is getting 24 VDC. Yes they hang up. But in the norm, when that happens, the green light will not come on. So, as LITD wrote, you need to take the top cover off and look at K1. The fat wire from the left side of K1 should be the input. Measure ACV from ground to all three wire. You should get 120 VAC on all three. Push S7, (AC output switch) up, the DS7 should light up. Then make the same measurements on the right side of the K1. What do you get?
 