I’m in the building stage now. Once it is wired I will determine if load shedding is needed. According to my calculations and using soft starts on my AC I may only need my pool equipment to be disabled during running. Thanks for all the info.Not getting a permit is one way to make sure it will pass inspection.
Just as a FYI for others reading the thread, saying its a portable generator doesn't get you out of the violation. If you have a MTS then its assumed you are also doing manual load management so its not an issue. If its an ATS the assumption is the generator could be subjected to the full connected load. Automatically connecting a source to a load its not able to handle is the problem.