Testing the DC voltage regulator in 5 easy steps
Step 1
With the set OFF, measure DC Voltage at the regulator wire that is marked with the red band. Should be around 24 to 24.5 volts DC...Is it??
Step 2
If so, DO NOT disconnect anything and start the generator. Now measure for DC Voltage at the regulator red banded wire again. This time it should be 26 to 28 volts DC give or take (in reality anything higher than you read with the set off will charge the batteries)...Is it?? If it is proceed to Step 3, If it is not skip to Step 5.
Step 3
If it is, measure the DC Voltage at the batteries positive and negative terminals. This voltage should be the same 26 to 28 Volts DC. If it is, then your charging system is working properly.
Step 4
If it is not, check the fuse located right above the oil filter canister; if it is bad replace it and test the voltage at the batteries again. If the voltage is now reading 26 to 28 volts everything is good.
Step 5
If you do not have 26 to 28 volts at the red marked wire on the regulator, with the set still running measure AC Voltage at the 2 leads coming from the stator under the blower wheel. This voltage should be around 33 volts AC +/-....is it??
If it is, then your regulator is not working. If it is not then your stator is possibly bad.
That's the jist of it, the charging system on these things is pretty straight forward
								Step 1
With the set OFF, measure DC Voltage at the regulator wire that is marked with the red band. Should be around 24 to 24.5 volts DC...Is it??
Step 2
If so, DO NOT disconnect anything and start the generator. Now measure for DC Voltage at the regulator red banded wire again. This time it should be 26 to 28 volts DC give or take (in reality anything higher than you read with the set off will charge the batteries)...Is it?? If it is proceed to Step 3, If it is not skip to Step 5.
Step 3
If it is, measure the DC Voltage at the batteries positive and negative terminals. This voltage should be the same 26 to 28 Volts DC. If it is, then your charging system is working properly.
Step 4
If it is not, check the fuse located right above the oil filter canister; if it is bad replace it and test the voltage at the batteries again. If the voltage is now reading 26 to 28 volts everything is good.
Step 5
If you do not have 26 to 28 volts at the red marked wire on the regulator, with the set still running measure AC Voltage at the 2 leads coming from the stator under the blower wheel. This voltage should be around 33 volts AC +/-....is it??
If it is, then your regulator is not working. If it is not then your stator is possibly bad.
That's the jist of it, the charging system on these things is pretty straight forward
 
				
 
 
		 
 
		
 
 
		 
 
		
 
 
		