• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

MEP-016E Proper wiring for a double receptacle outlet

pahunter

Member
33
1
8
Location
Lock Haven/pa
Could someone please post on the proper way to wire this generator for a double receptacle outlet, not directly connected to the house. I read to hook L1 and L2 to hot on each receptacle and connect neutral to the frame. Nothing goes to the L0 or L3?
Also, about how many amps can you draw on L1 and L2?
Thank you.
 

Ray70

Well-known member
Steel Soldiers Supporter
2,925
7,116
113
Location
West greenwich/RI
In your case it sounds like you want straight 120V not 240 split into 2 legs as you describe above.
I believe there should be a sticker on or near the clear cover over the lugs that tells you where to set the selector switch and where to hook up your wires. I know the 016 is different than most others like 002/003 802/803.
Should also be listed in the TM.
 

Guyfang

Moderator
Staff member
Moderator
18,093
27,154
113
Location
Burgkunstadt, Germany
Indeed! Look in the TM. Its there, looked at it a few months ago. If you don't have the TM's, download them from the TM section in SS. If you need help, say something
 
Top