MEP-803a overload circuit

jamawieb

Well-known member
1,435
557
113
Location
Ripley/TN
Ok, so before I go burn my garage down with everything in it....

So I swapped the K8. All of the wires appeared to be put in place correctly (and I believe I did my due diligence in putting them all back in position)...

So now I have NO power at the set at all. The dead crank works... but when I cycle the start switch, nothing. No panel lights either. No fuel pumps running. Nothing.

Might I just have a bad replacement? Any other thoughts? I've got a terrible case of laryngitis right now, and I've been out in the garage for like 3.5 hours now (should be relaxing).. so this is literally the last thing I need.
Something your missing when you removed K8. K8 wouldn't effect the 24volt system. Did you check CB1 (DC breaker) and make sure your battle short is not on. DC powers goes to CB1 then emergency stop then to the master switch.
 

Guyfang

Moderator
Staff member
Moderator
16,933
24,612
113
Location
Burgkunstadt, Germany
LID,

Stop. Take a breather. There are two possible reasons it won't work.

You mis wired it. If it ran before, it should if you wired it right.
It has more then one problem.

So, re check the K8 wires.
Then start at the start. Go to the S1, and troubleshoot like I know you can. Do not try and figure out why, do the troubleshooting. Find out why it won't start.

If you hit a stone wall, put the old K8 back in. See if it starts, but only last resort.

Are you sure it's the right K8? Part number matches?
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,863
6,093
113
Location
MA
I must have hit the emergency stop when reassembling the control box hinge... **** do I feel dumb. I owe kloppk a six pack, I think. I was so frustrated (I've had this laryngitis for like 3 weeks now) that it had taken that long to do the swap over (though I was very certain to make sure to double check the schematic to make sure each position was located properly).

She runs. I'll see if the new part clears up the concerns tomorrow. Thanks all.
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,863
6,093
113
Location
MA
It happens to the best of us.

What's the third step in the troubleshooting diagram, in the -10 manual, for: Will not crank?

I believe that would be "Open -10 manual" ;). I just dropped the project and came in for lunch and to post the question, experiencing ultimate frustration. You finally shake your sickness?
 

Guyfang

Moderator
Staff member
Moderator
16,933
24,612
113
Location
Burgkunstadt, Germany
It's much better. But still not right. The Frau Doctor, (she is from Mongolila) gave me antibiotics because she thinks I may have a touch of bronchitis or pneumonia. So we shall see. The weather has warmed up and i took a short ride on my bike, with everyone and his dog in disagreement. Just could not see it, when the temp is almost 20 c. And the streets dry. Need to get my wind back.
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,863
6,093
113
Location
MA
20c sounds like a wonderful temp for a ride! I used to head west every winter for a round of trade shows, in the process, trading New England February for mid 60s Southern California. The locals would be scurrying around in coats... I'm just looking for a nice outdoor cafe to grab a bite at to enjoy the wonderful weather!
 
Last edited:

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,863
6,093
113
Location
MA
So, the new K8 did not fix the problem. It is still going into overload condition. AND.. I have pneumonia. Fun all around.

Getting 12-18" of snow tonight, so I have it out back, knowing it will run our place just fine until I can get back to it (we have very little draw requirement).
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,863
6,093
113
Location
MA
Oh yeah, great combo. By the time I came back from the doctors office around noon, my wife had prepared a bone broth for me. She's a keeper.

My next guess as to what the problem might be here, are the burden resistors. Thoughts?
 

kloppk

Well-known member
Steel Soldiers Supporter
2,169
3,622
113
Location
Pepperell, Massachusetts
Possibly...
When you are running at 100% load the voltage across R10, R11 & R12 ought to be ~5.6 VAC based on my calculations.
Or if at 50% load ~2.8 VAC.
Check it if you get a chance the next time you run it at one of those loads.

I too am looking at 12-20" of snow over here in Pepperell, MA.
 

CapePrep

Active member
267
196
43
Location
MA
Light, Kloppk helped me with these same tests and he is dead on with his calculations for testing the resistors. I tested mine and ruled them out. He suggested I get another overload relay and it solved my issue. I had the 802 up to 32 amps for short periods this past weekend. I also think cleaning S8,etc with contact cleaner and cycling them helped. You will find the solution.
Possibly...
When you are running at 100% load the voltage across R10, R11 & R12 ought to be ~5.6 VAC based on my calculations.
Or if at 50% load ~2.8 VAC.
Check it if you get a chance the next time you run it at one of those loads.

I too am looking at 12-20" of snow over here in Pepperell, MA.
 

Guyfang

Moderator
Staff member
Moderator
16,933
24,612
113
Location
Burgkunstadt, Germany
So, the new K8 did not fix the problem. It is still going into overload condition. AND.. I have pneumonia. Fun all around.

Getting 12-18" of snow tonight, so I have it out back, knowing it will run our place just fine until I can get back to it (we have very little draw requirement).

We have pneumonia. Mine is according to Frau Doctor not too advanced. Not good.

After looking at the burden resistors, if they are good, look at the CT's, and maybe see if they are wound properly.
 

jamawieb

Well-known member
1,435
557
113
Location
Ripley/TN
The interesting problem is that its disconnecting the load even with the battle short on. Something is breaking the current flow from the interrupter switch to the K1 contactor. Usually with a bad burden resistor, you will get an overload fault and is easily bypassed by the battle short. I still say someone was messing around in the control cubicle and connected wires incorrectly. My guess is something connected wrong on K1 or S8.
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,863
6,093
113
Location
MA
Ok, so I misspoke (or was not clear). So the overload light was still coming on. I did not take the additional step of running with the battle short on (I really shouldnt have been out there messing with the set to begin with, so I wasn't going to push my luck). I will though, and will check the CTs, K1, and S8. All more work I did NOT intend on...
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,863
6,093
113
Location
MA
Ok so riddle me this, Batman...


So I have a little bit of time to play with this today. Just hooked up the bank, and got it to temp and flipped it on. So I am getting about 8 minutes of run under load (about 75% on the gauge, about 10.8kw of dryer element). So the generator is still disconnecting power, but now I am not getting an overload light... Battle short is off still, as it should not effect this test (as the idiot light panel is not part of the equation now).

Hmm...
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,863
6,093
113
Location
MA
It was also doing this when testing 5.4 + 2.7kw.

Does anyone have a simple wire schematic for the S8 that is cleaned up? What seems more likely here... something is miswired on the S8, or that the S8 might be faulty?
 

Guyfang

Moderator
Staff member
Moderator
16,933
24,612
113
Location
Burgkunstadt, Germany
Wire numberFromTo
002AS08-02TB3-2
008AS08-03TB3-8
010AS08-08TB3-10
004AS08-09TB3-4
167BS08-13TB4-1
179BS08-14P6-32
006AS08-20TB3-6
007AS08-22TB3-7
012AS08-26TB3-12
005AS08-32TB3-5
011AS08-36TB3-11
009AS08-38TB3-9
167AS08-41TB4-1
176CS08-43P6-12
162BS08-44P6-7
160BS08-45P6-8
177BS08-46P6-10
175BS08-47P6-9
001AS08-L1TB3-1
001BS08-L1K1-A1
002BS08-L2K1-B1
003AS08-L3TB3-3
003BS08-L3K1-C1
006BS08-LOTB2-LO
006DS08-LOTB4-4


How is that? Works? SO8 is S8
 

Light in the Dark

Well-known member
Steel Soldiers Supporter
3,863
6,093
113
Location
MA
That's awesome Guy, the forum thanks you.

I took the operator cover off this morning, and set to checking all TBs, all connections, and to bathe the S8 in deoxit, like it was visiting a Turkish spa. I found two wires on a TB that were not loose, but could take an additional 1/16th of a turn. I thoroughly sprayed the S8, and let flare off.

I wheeled the set back to my testing area, threw the top back on, and let it get up to temp (nothing moves too quick in -18C, myself included). I proceeded to put load on it, and I think we have success. It took 10.8kw with no sign of stopping, and I ran it at the full 13.5kw resistive for 20 minutes, and she is still purring.
 