MEP-804B Overvoltage Shutdown

Guyfang

Well-known member
8,988
3,316
113
Location
Burgkunstadt, Germany
Well, then we need to see what Arty gets from the test.
Guyfang thank you for jumping in. Sorry stupid question, how do i reset? Below I will post the results of the test of A1 and the voltage pot seperately.
On the fault indicator panel is a reset switch. If you do not reset the fault, the indicator continues to shut the set off for the same fault. You can also pull the plug on the fault indicator panel, and try and start the set. Will it funtion properly? Keep in mind, all safety functions are now bypassed. But shortly, for troubleshooting, it should not be a problem.
 