I am looking into getting a MEP-806A for an industrial application that would require 3 phase 480V. I can look up the specs on the 806 and see that it can produce 240/416 3 phase but it appears that it can be "tunned" up to reach 480V on the 60Hz side.
Am I reading this correctly?

Thank you,
Corey
 

155mm

Chief and Indian
Steel Soldiers Supporter
1,246
506
113
Location
Guymon, OK
I will make a small bet, whatever you have that is 3ph 460 will accept 416 and its amp draw will be 2-3 more amps than 460
 

Guyfang

Moderator
Staff member
Moderator
18,154
27,274
113
Location
Burgkunstadt, Germany
At last! Someone who doesn't want to change a perfictly good three phase get set, to a single phase boat anchor. We still got to keep an eye on him. Ordnance Guy. Shady, indviduals.
 

04mustang

Member
349
10
18
Location
Lumberton/NC
lol, thank you all for the comments. What I am looking at powering is a series of pump motors. The most of which would be 50hp. and not more than 1 at a time.
 

155mm

Chief and Indian
Steel Soldiers Supporter
1,246
506
113
Location
Guymon, OK
Are you sure you need a 60kw for 1 50hp motor?

If i remember correctly, a 60kw is 200amps per leg, and a 50 hp 3ph motor only pulls like 95 amps, I might be smokin left handed cigarettes this morning though
 

04mustang

Member
349
10
18
Location
Lumberton/NC
So your saying that I could get by with a 30kw unit? because that's the only 2 choices if going the military route. I agree with you and felt like 50kw would be a better fit.
 