my MEP-831A runs good when it runs, but it has a bad startup issue. Preheating up to 45 seconds didn't make a difference. I was sick about the bad startups and thought the fuel is running backwards. But every manual startup attempt was a very successful attempt with no issues at all so i am wondering more and more... months over months are gone... the comparision to a construction machine's diesel engine or a mower was the forewarding idea: first we open the gas throttle to idle speed, then we crank the engine. The magnetic actuator is held by the magnet to close the throttle to stop the engine. But it is held during startup and after cranking a long minute it release and then the engine can run (!) - what is defective on the controller? Is there a relay contact worn? Or is this a problem of the controller (he must give a current on the coil of the actuator on RUN-Position to immediate release the actuator from the magnet, but it won't work)? When i pull it manually away from the magnet, it starts up on starter position immediately with no issues as like in manual startup procedure. Had you found a healthy solution for this (i don't want to pull the actuator off the magnet manually every startup; because i want to let a plc decide to autostart up and stop the genset).