% load guage working now

Trace the wires back from the output breaker and make sure they are running through the CT loops. Someone may have rewired it at some point and forgot to run the new wires through the loops.

Ike
Thanks Ike. The generator is currently connected to the shop providing power to the 220v panel and for the last 45 minutes the % load guage is working again as it should. I'll leave well enough alone for now and will report back with any changes.

David
 

reset2

Active member
197
100
43
Location
Myersville MD
Any updates since 2011. Just learning about these gensets. Have one in the start up phase. Broke the governor linkage plastic ball socked and looking to replace when I get a chance.
 

Ray70

Well-known member
Steel Soldiers Supporter
2,895
7,030
113
Location
West greenwich/RI
So David, I see the problem with you %Load meter "fixed itself", how did you make out with adjusting the droop on your governor? Did you get it within spec, or is there some other problem causing excessive droop under load?
 