MEP006A
bruce1776
Illinois
on the metal can relays (k5, k6 etc.) I don't see any labeling, but I do see a pin that is different is that pin to be on the top or bottom when installing?
bruce1776
Illinois
Did you do what I wrote in post #16?
I did do that, and nothing. I put the new Watt Transducer in and a new A11 excitation box I bought in and fired it up and meters moved, but it would not stay running unless I put on the Battle Short. So with the battle short on I dialed in the voltage to 208/120 but the frequency would not go below 61hz. Not saying that a new A11 couldn't have bade parts, but it is brand new. I will have to look at tomorrow as I do have a new VR as well, is there anything else I should look at?
bruce1776
Illinois
Volt reg card is bad, in the A11.
I changed the V Reg and now I have nothing, dials go freq and vol go up and then they go down, I put the original VR in and I am back to voltages and freq ok, but have over voltage light on and have to run in Battle Short
bruce1776
Illinois
I am not sure what is happening to my replies, because I don't see them here. I changed the VR in the A11 and when I started the unit up the freq and voltage gage went full dial then to nothing, I put the original VR back in the A11 and I am back to good voltages and freq but only in Battle short, the difference I see this time is my fluke and on board measuring are different my fluke says 208 and the onboard says 183.
Guyfang
27,331
Burgkunstadt, Germany
I changed the VR in the A11 and when I started the unit up the freq and voltage gage went full dial then to nothing, (This tells me that the S9 is sending inital excitation to the Main gen. Thats good. The volts/hertz drops off because the A11/VR is not taking over.) I put the original VR back in the A11 and I am back to good voltages and freq but only in Battle short, the difference I see this time is my fluke and on board measuring are different my fluke says 208 and the onboard says 183.
Do you have two A11's and two VR's?
bruce1776
Illinois
I have the other A11 from my other gen, I am sending the new VR back to where I bought it for replacement. What senses the voltage and sends the signal to the Tac relay, could any of that circuit be bad?
Guyfang
27,331
I dont think so.
If you have an A11 that works right, try it in your problem gen set. Every time you put another A11, or Vr in the set, you have different problems.