Hello all. I am having a few issues with my gen set.
When I start the gen, I will get a 'under voltage ' light. Someone has messed with the k5 relay before, it was not bolted to the base and loosely in there.
IMG_9776.JPG
They may have replaced it or put a faulty one in.
I cheched the magnetic sensor on the bell housing and it checks out ok.
This morning I checked the fuse in the control box and I thought it was ok.
This evening I checked again and it was open. So I have to replace it. i think it is a 3 amp fuse but not sure I cant see any writing on it.
IMG_9779.JPG
Can someone verify the value?
IMG_9778.JPG
 

Guyfang

Moderator
Staff member
Moderator
18,063
27,093
113
Location
Burgkunstadt, Germany
Install a 3amp/600VAC, time delay fuse. The attached document explains the who, what and why of the quad circuit .MWO. If the new fuse blows, you have a volt regulator problem.

Go to the -24 TM, page, (PDF reader page #) 213, for the test procedure for the K5.
 

Attachments

319cssb

Well-known member
1,019
221
63
Location
Easley SC
Install a 3amp/600VAC, time delay fuse. The attached document explains the who, what and why of the quad circuit .MWO. If the new fuse blows, you have a volt regulator problem.

Go to the -24 TM, page, (PDF reader page #) 213, for the test procedure for the K5.
The # amp fuse I replaced the old one with didn't blow.
I see a different oddity : the gen set has under voltage light on. The AC switch doesn't close, stays open. I got my environment unit connected to the 3 phases. I have to turn on the battle switch and then close the AC connect switch and it stays closed.
If I turn on the gen set and the under voltage light is on and I press the test button, the over voltage will come on and turn off the gen set.
Lately I am getting a reading on the gauges. ODD ... however I can't adjust the voltage.
Can someone post a photo of what the connections on the voltage regulator should look like?
I will post a photo of what mine looks like when I get home.
 

Guyfang

Moderator
Staff member
Moderator
18,063
27,093
113
Location
Burgkunstadt, Germany
The # amp fuse I replaced the old one with didn't blow.
I see a different oddity : the gen set has under voltage light on. (What the AC volt meter read? What voltage do you have at the 120 outlet?) The AC switch doesn't close, stays open. (If, there is no output from the main gen, then the K1 will not close.) I got my environment unit connected to the 3 phases. I have to turn on the battle switch and then close the AC connect switch and it stays closed. (You are forcing it to close, so it will close. And stay closed)
If I turn on the gen set and the under voltage light is on and I press the test button, the over voltage will come on and turn off the gen set.
Lately I am getting a reading on the gauges. ODD ... however I can't adjust the voltage.
Can someone post a photo of what the connections on the voltage regulator should look like?
I will post a photo of what mine looks like when I get home. (Open the attached document. On page 5, (PDF reader page number) is the A1, (AC volt regulator) hook up.)
Open to read all I wrote.
 