• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

MEP831A - Overvoltage Fault

DieselAddict

Well-known member
Steel Soldiers Supporter
2,531
2,058
113
Location
Efland, NC
I have an 831 that will give an overload fault upon startup if I leave it out in the rain. To resolve the issue I will let it run for 15 or 20 minutes. The heat from the engine will dry out the inverter. I can then cycle the power on the unit and it will run OK.

When I have some free time I'm going to pull the inverter and dry it out in the over then seal everything up. Hopefully that will stop the problem.
 

kloppk

Well-known member
Steel Soldiers Supporter
2,138
3,514
113
Location
Pepperell, Massachusetts
The inverter actually has two 120 volt inverters inside of it. In 240 mode it internally connects the two inverters in series and sets them them to be 180 degrees out of phase to generate the 240.
In 120 mode the two inverters inside are connected in parallel and are in phase with each other.
Sounds like one of the two inverters has an issue.
If you do open up the inverter you ought to look for anything abnormal such as the tops of the large black capacitors bulging or split open.
Also there are 4 small black fuses on the circuit board where P15 and P16 connect to the inverter. Those sometimes blow causing issues.
 

CommieGIR

Member
26
38
13
Location
Cheyenne, WY
Hey KloppK,

So on the back of the inverter controller board, there's two connectors that come off going to the transformer/capacitor board and they look like they got a little hot. Any idea if that's normal?
 

CommieGIR

Member
26
38
13
Location
Cheyenne, WY
So its reliably putting out 240v now, but still has the overvolt fault.

I've noticed when load drops off, it loses one leg until the engine revs back up with a new load. An odd issue, but it functions, will certainly not expect it to handle a full 3kw load.
 

loosegravel

Just a retired mechanic who's having fun!
504
891
93
Location
Enumclaw, Washington
So its reliably putting out 240v now, but still has the overvolt fault.

I've noticed when load drops off, it loses one leg until the engine revs back up with a new load. An odd issue, but it functions, will certainly not expect it to handle a full 3kw load.
More will be revealed! Good work so far.
 

kloppk

Well-known member
Steel Soldiers Supporter
2,138
3,514
113
Location
Pepperell, Massachusetts
Did you check the 8 fuses while you had it apart? Those fuses are the input fuses for the two inverter power supplies. If any were blow an inverter wouldn't get the full AC power from the PMA.

The circuit board they are on also contain about a dozen high current diodes to rectify the 3 phase AC from the PMA to DC. Sometimes 1 or more of those diodes can blow messing up the rectification.

The large black caps are on the DC output to smooth the DC.
 

CommieGIR

Member
26
38
13
Location
Cheyenne, WY
I get the feeling this thing was in depot, a lot of the screws securing the coupling between the boards for the loads were loose. All the fuses you mentioned KloppK were intact and ohmed out good, so who knows.

But it functions as a generator, and that'll do.
 
Last edited:

CommieGIR

Member
26
38
13
Location
Cheyenne, WY
Well that was short lived, now it starts and runs but then even with the Fault Controller disconnected its cutting power to the GC via K12, even though it appears to be showing good voltage out.

That Regulator/Converter really is the weakpoint in this thing.
 
Last edited:
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website like our supporting vendors. Their ads help keep Steel Soldiers going. Please consider disabling your ad blockers for the site. Thanks!

I've Disabled AdBlock
No Thanks